My SMX3000 UPS has suddenly reported "an inverter fault exists". The panel shows a red LED. The outputs are turned off. The fan is no longer running.
The NMC events log reports are as follows:
Date Time User Event
08.08.2016 15:53:07 Device UPS: The output power is turned off.
08.08.2016 15:53:07 Device UPS: An inverter fault exists.
08.08.2016 15:53:06 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
08.08.2016 15:53:06 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
08.08.2016 15:53:06 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
08.08.2016 15:53:05 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to turn on, sequenced.
08.08.2016 15:53:05 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn on, sequenced.
08.08.2016 15:53:05 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn on, sequenced.
08.08.2016 15:52:53 Device UPS: The output power is turned off.
08.08.2016 15:52:53 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
08.08.2016 15:52:53 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
08.08.2016 15:52:53 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
The UPS "about" information is as follows:
Model Smart-UPS X 3000
SKU SMX3000RMHV2UNC
Serial Number IS1309004233
Firmware Revision UPS 06.8 (ID23)
Manufacture Date 27.02.2013
Apparent Power Rating 3000 VA
Real Power Rating 2700 W
Internal Battery SKU APCRBC117
External Battery SKU APCRBC118
Attempting to reset the UPS by powering off the input feed, removing all batteries, re-installing the batteries and re-applying input power gives the same result - the fan runs briefly, then the UPS shuts down reporting an inverter fault.
Is there anything I can usefully check or reset ?
Cheers, Colin.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:52 AM . Last Modified: 2024-03-18 04:01 AM
Hello Colin,
I am sorry to hear that you are experiencing issues with your APC unit. Based on your description and the logs you pasted, it looks like there is an inverter fault. That being said, it looks like you completed the "braindead" process, by removing all power sources and load to reset the internal processor. The fact that this did not clear it means, that it is probably not a false positive and the UPS should be replaced asap. After putting the serial number in our system, it looks like it is right around the cusp of being out of factory warranty. I would advise calling into Technical Support at 800 800 4272 and explain to them the fault and what you have done.
If you have any other questions, please feel free to post them here or ask technical support.
Thanks,
Shanon
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:52 AM . Last Modified: 2024-03-18 04:01 AM
Thank you. Support call made. It appears to be a "hard fault". Warranty replacement has been arranged.
Cheers, Colin.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:52 AM . Last Modified: 2024-03-18 04:01 AM
Hello Colin,
I am sorry to hear that you are experiencing issues with your APC unit. Based on your description and the logs you pasted, it looks like there is an inverter fault. That being said, it looks like you completed the "braindead" process, by removing all power sources and load to reset the internal processor. The fact that this did not clear it means, that it is probably not a false positive and the UPS should be replaced asap. After putting the serial number in our system, it looks like it is right around the cusp of being out of factory warranty. I would advise calling into Technical Support at 800 800 4272 and explain to them the fault and what you have done.
If you have any other questions, please feel free to post them here or ask technical support.
Thanks,
Shanon
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:52 AM . Last Modified: 2024-03-18 04:01 AM
Thank you. Support call made. It appears to be a "hard fault". Warranty replacement has been arranged.
Cheers, Colin.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:52 AM . Last Modified: 2024-03-18 04:01 AM
The UPS has been replaced under warranty. The replacement UPS is working normally. Good service by APC.
Cheers, Colin.