SMT3000RM2U Battery Replacement
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-01-1306:38 AM
The battery cartridge is hot swappable so no need to power down or disconnect any loads.
Remove the six retaining screws from the front case. Disconnect the battery cable and remove old battery cartridge.
Insert the new battery cartridge and reinstall the six screws. Reattach the battery cable and wait for the system to prompt you to indicate if this is a new battery cartridge.
Toggle from No to Yes and enter the month and year than hit save. Wait for the system to indicate the battery is 100% SOC (State of Charge).
Once it indicates 100% SOC manually initiate a Self Test either through the LCD / NMC.
Let it complete, pass, and battery cartridge return to 100% SOC. Manually initiate a battery calibration with at least 30% attached load and let the process complete.
Doing this step is critical to allow the system to know and display the correct operational runtime.
Lastly, mark the battery installation date physically on the cartridge with a sticker / sharpie.