SMT1000I USB coonection/comms not working? Correct Serial cable? Firmware update

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1000I USB coonection/comms not working? Correct Serial cable? Firmware update
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Aficionado
Crewman Aficionado
Crewman

Posted: ‎2025-03-22 02:49 PM

0 Likes
3
502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-22 02:49 PM

SMT1000I USB coonection/comms not working? Correct Serial cable? Firmware update

SMT1000I
FW 9.03 ID:18

Usb B -to- USB A cable
plugging into several usb ports..... does not make it appear under lsusb
modbus enabled/disabled makes no differnece.

ressetting UPS to factory defaults makes no difference

firware update tool does not see it either
Communication/control is supported over usb B -to- Usb A correct?

Please advise, I am stumped (UPS Newbie)

would updateing to firmware 15 solve the issue? (ID:18 syas it supports FW update over USB)

is this the correct RJ45 to serial cable?
https://www.apc.com/us/en/product/AP940-0625A/cable-ups-communications-smart-signalling-6-2m-db9-to-...

Is rj45 -to- usb not compatible?  I have no serial ports

I have no serial ports, could it be converted back to usb A on the other end? (if usb A -to- usb B does not work?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Aficionado
Crewman Aficionado
Crewman

Posted: ‎2025-03-25 02:29 AM

In response to Teken
0 Likes
1
446
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 02:29 AM

Thank you for the feedback

TL;DR - 3 out of 4 faulty usb b-to-usb a cables were the issue. fourth one finally worked. all is well now

I realise now that It could have been a clearer post....was done in haste amidst troubleshooting and frustration

 

The ultimate goal was to ewstablish communication with the computer and ultimatlet begin setting the ups up. but the communication was not happening
This model has rj45, usb as ways to connect and communicate with Server/computer (and optional NMC for Management)
Whilst plugging in the usb B to usb A cable into the computer it would not show up or be recognised
I had tried several times and ways to do so, as mentioned (rather confusingly I admit) in my initial post
I had also tried plugging it into a windows machine to see if it was being picked up and nothing


The firmware tool was just a way, I thought, I could test to see if it actually communicates with the machine, just in case for some reason it wasn't being picked up by the other means

The question about the serial cable was to confirm the model so I could find one and troubleshoot the connection issues through that also, to eliminate guesswork

Alas.....in the end it was faulty cables............I had tried THREE (yes 3) separate usb b-to-usb a cables before posting here and they all apparently failed.

As a last attempt I sourced a fourth one and it all showed up on the host machine as expected.
1 out of 4 cables...never came across those odds ...the 3 duds have been disposed of

Regarding the firmware update....followed the instructions and everything went smoothly . I am now on FW 15.0. (I had already done this before your response, judging by your warnings it seems I got lucky that it all went well - hardware is not under APC warranty)

Thank you for the insight and info

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2025-03-24 04:59 AM

0 Likes
2
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 04:59 AM

You’ll need to restate what the actual problem is and your ultimate goal as I have no clue what you’re asking or saying.

 

Regardless, the link you provided is the correct RJ50 to Serial cable.


You can use a serial to USB adapter if you don’t have a computer that has this legacy port.

 

This is a proven model that works to convert the signal correctly once the USB Driver has been installed:

 

https://a.co/d/hv4g3Vf

 

Lastly, insure your environment meets all the requirements and prerequisites before you attempt a UPS firmware upgrade! ☝️

 

If the hardware is under APC warranty this procedure should be done over the phone live with APC Technical Support.

 

Have a back up and exit plan should things go bad.

 

If the hardware is (Not) under warranty you better understand the risks of upgrading the UPS firmware. 🤦‍♂️

 

Questions Ask . . . 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

Aficionado
Crewman Aficionado
Crewman

Posted: ‎2025-03-25 02:29 AM

In response to Teken
0 Likes
1
447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 02:29 AM

Thank you for the feedback

TL;DR - 3 out of 4 faulty usb b-to-usb a cables were the issue. fourth one finally worked. all is well now

I realise now that It could have been a clearer post....was done in haste amidst troubleshooting and frustration

 

The ultimate goal was to ewstablish communication with the computer and ultimatlet begin setting the ups up. but the communication was not happening
This model has rj45, usb as ways to connect and communicate with Server/computer (and optional NMC for Management)
Whilst plugging in the usb B to usb A cable into the computer it would not show up or be recognised
I had tried several times and ways to do so, as mentioned (rather confusingly I admit) in my initial post
I had also tried plugging it into a windows machine to see if it was being picked up and nothing


The firmware tool was just a way, I thought, I could test to see if it actually communicates with the machine, just in case for some reason it wasn't being picked up by the other means

The question about the serial cable was to confirm the model so I could find one and troubleshoot the connection issues through that also, to eliminate guesswork

Alas.....in the end it was faulty cables............I had tried THREE (yes 3) separate usb b-to-usb a cables before posting here and they all apparently failed.

As a last attempt I sourced a fourth one and it all showed up on the host machine as expected.
1 out of 4 cables...never came across those odds ...the 3 duds have been disposed of

Regarding the firmware update....followed the instructions and everything went smoothly . I am now on FW 15.0. (I had already done this before your response, judging by your warnings it seems I got lucky that it all went well - hardware is not under APC warranty)

Thank you for the insight and info

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-03-25 10:51 AM

In response to Aficionado
0 Likes
0
443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 10:51 AM

The three cables were not defective they simply did not have the data cable present! ☝️

 

The market is filled with power only vs data & power USB cables. This problem has existed since the USB standard was introduced. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore