SMART UPS 3000 RM
  • SMART UPS 3000 RM
Posted: ‎2021-06-28 06:29 AM . Last Modified: ‎2024-03-18 01:29 AM
592
SMART UPS 3000 RM
Hi all,
Since 2 days i am receiving "Code: 0x0109 Warning - UPS: On battery power in response to an input power problem." on one of our devices. A SMART UPS 3000 RM. Within in a few seconds the warning is resolved by: "Code: 0x010A Informational - UPS: No longer on battery power.".
The powercircuit isn't giving any other problems on other devices.
Questions:
  • Can devices of this type give this error by old age? The device is already 6 years old;
  • Is it harmful for the device?
  • Could it be possible that it does come from a faulty net?
  • Is it wise to measure the power quality or to just buy a new device?
Any ideas to handle these warnings?
Thanks in advance, Kees
It is possible it is due to age. Have you tried to adjust the sensitivity level of the unit. If the unit is set for high sensitivity adjusting it down to medium or low may resolve the warnings.
No. The only issue is the more frequently the UPS uses the battery the sooner the battery should be replaced.
Yes. You should measure the power to be sure there is no issue on that circuit or outlet. If the power quality is good and adjusting the sensitivity does not resolve the issue than at that point it may be a good time to replace the unit.