Requesting data for monitored temperatures vs. failure rates over time

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Requesting data for monitored temperatures vs. failure rates over time
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

0 Likes
3
848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

Requesting data for monitored temperatures vs. failure rates over time

My company performs remote monitoring for a several hundred APC  UPS'  covering a variety of models attached to various systems we administer or maintain, primarily (but not solely) at customer -  or otherwise remote - sites utilizing a 3rd party monitoring platform. In short, what we'd like to be able to do is set a threshold on our monitoring software to alert when a battery reaches a temperature that will serve to provide advance notice of a battery whose capacity is beginning to diminish irrevocably - but isn't there yet - so we can be prepared in advance to replace them, rather than only after an actual alarm has occurred and causing the customer to have to deal with it.

I am led to understand that a battery's average stable temperature will increase  once its total capacity begins to decrease below a certain threshold - even if average ambient temps do not change - and would like to know if there is any data available on average/observed temperatures vs. capacity over time with the additional data point of mean total failures along those time-lines? I understand, of course, that ambient temperature will have an effect on this, but whether the data includes ambient temps, or is just a controlled environment, the information would be useful to us to establish a baseline understanding of the temperatures that might affect - or be predictive of - future battery performance or failure so we can set monitor thresholds to that end.

Thank you very much,

C.J.

Labels
  • Labels:
  • Other Environmental Monitoring Products & Questions
  • Tags:
  • capacity
  • failure
  • temperature
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

Temperature is not a reliable method to do what you want to do.

Yes, *some* battery failure modes cause increased dissipation, but not all. In my experience maybe 5-10% of batteries fail by developing an internal fault that cooks the battery from the inside out. The remainder simply gradually lose capacity and develop higher internal resistance until the UPS screams "enough!".

To be honest, probably the best way of monitoring what you want to monitor would be to keep tabs on the battery constant in a SmartUPS. As the UPS does it's cycles & tests, it keeps track of the battery capacity under load (as this is what it uses to provide runtime estimates). This drops in concert with the estimated battery capacity. This does not detect pending catastrophic failure however. It goes without saying there is no way to easily expose this value without delving into the old UPSLink protocol, and newer UPS hide this internally so you can't get to it anyway.

If you were to run a prediction, you'd use temperature, load & projected runtime. The combination of load & projected runtime can be reversed with a bit of maths and an estimate at peukerts constant to give you a vague measure of actual battery capacity, and battery float life is significantly reduced at elevated temperatures (see any and all SLA battery data sheets for the graphs).

I did an exercise recently where I took a stack of UPS, got the load & runtime values and reversed that back into battery capacity, then replaced the batteries and actually measured the units that came out. In most cases the calculations reflected the actual battery capacity within about 10%, and all were better than 20%. SNMP and a bit of python would do that for you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

Bump please for reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

0 Likes
0
849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

C.J.,

This sounds more like a battery tech question than a UPS question, so I guess that it can be better answered by people working with batteries every day - there may be some here that have enough experience from past issues and personally I have had my own list of failures from batteries in string-applications and as you indicated, a battery (cell) that is getting low in capacity will be prone to heat up, especially if it gets discharged to polarity reversal, which then accelerates the capacity loss. I have not seen this (yet) in my UPS, but have had to deal with it in my EV.

Note that the heating up does not occur (much) in shallow charge/discharge unless the internal resistance of the cell is significantly increased, then you may see additional heating, but my experience is that it especially presents itself during a longer discharge test, since that brings the weaker cells into deep discharge with the resulting additional heat generated.

Note that another failure mode: bad connection or cable contact also results in heat, so it makes sense to measure close to the terminals of the batteries. Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 09:28 PM . Last Modified: ‎2024-03-19 04:28 AM

Temperature is not a reliable method to do what you want to do.

Yes, *some* battery failure modes cause increased dissipation, but not all. In my experience maybe 5-10% of batteries fail by developing an internal fault that cooks the battery from the inside out. The remainder simply gradually lose capacity and develop higher internal resistance until the UPS screams "enough!".

To be honest, probably the best way of monitoring what you want to monitor would be to keep tabs on the battery constant in a SmartUPS. As the UPS does it's cycles & tests, it keeps track of the battery capacity under load (as this is what it uses to provide runtime estimates). This drops in concert with the estimated battery capacity. This does not detect pending catastrophic failure however. It goes without saying there is no way to easily expose this value without delving into the old UPSLink protocol, and newer UPS hide this internally so you can't get to it anyway.

If you were to run a prediction, you'd use temperature, load & projected runtime. The combination of load & projected runtime can be reversed with a bit of maths and an estimate at peukerts constant to give you a vague measure of actual battery capacity, and battery float life is significantly reduced at elevated temperatures (see any and all SLA battery data sheets for the graphs).

I did an exercise recently where I took a stack of UPS, got the load & runtime values and reversed that back into battery capacity, then replaced the batteries and actually measured the units that came out. In most cases the calculations reflected the actual battery capacity within about 10%, and all were better than 20%. SNMP and a bit of python would do that for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of