Receiving the "The Application Was Not Able to Load" message after failed ON-1571 firmware upgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Receiving the "The Application Was Not Able to Load" message after failed ON-1571 firmware upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Steeltown
Crewman Steeltown
Crewman

Posted: ‎2025-05-05 09:43 AM . Last Modified: ‎2025-05-05 11:56 AM

0 Likes
3
1433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-05 09:43 AM . Last Modified: ‎2025-05-05 11:56 AM

Receiving the "The Application Was Not Able to Load" message after failed ON-1571 firmware upgrade

Greetings
I have an APC SCL500RM1UNC Smart-UPS with an integral ON-1571 network management card.  I tried upgrading the ON-1571's firmware to 2.5.3.2 but the firmware upgrade utility stopped with the following error:


[05/05/2025 11:33:38] NMC Firmware Update Utility v1.0.4 initialized.
[05/05/2025 11:33:54] Downloading and verifying configuration file from 10.***.***.***, please wait...
[05/05/2025 11:33:55] Firmware distribution does not match target device platform; this could be due to a corrupt distribution.
[05/05/2025 11:33:55] Uploading firmware file 1 of 1: Firmware Image to 10.***.***.***, please wait...
[05/05/2025 11:33:55] Unable to update device 10.***.***.*** with Firmware Image; stopping all further processing of this device!

 

I can still SSH into the card.  Here's the About info from that:

apc>about
E000: Success
Hardware Factory
---------------
Model Number: 0N-1571
Serial Number: 5A2429T34902
Hardware Revision: 3
Manufacture Date: 07/17/2024
MAC Address: 28 29 86 A2 B1 87
Management Uptime: 0 Days 1 Hour 9 Minutes

Application Module
---------------
Name: sucan
Version: v2.5.3.2
Date: Oct 03 2024
Time: 14:54:02

APC OS(AOS)
---------------
Name: aos
Version: v2.5.3.2
Date: Oct 03 2024
Time: 14:54:02

APC Boot Monitor
---------------
Name: boot
Version: v1.5.4.1
Date: Jun 4 2024
Time: 16:20:19

apc>

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Steeltown
Crewman Steeltown
Crewman

Posted: ‎2025-05-06 01:02 PM

In response to Teken
0 Likes
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 01:02 PM

Solved the issue by

SSH into NMC

Enabling ftp on NMC

Using ftp to put

apc_hw21_su_2-5-4-4.nmc3

onto the ON-1571 NMC.  After rebooting the NMC, I was then able to successfully run the v2.5.4.4 Firmware Update Utility.  The key is that this model ON-1571 NMC is only compatible with _su_ firmware.  I had tried to upgrade to a _sucan_ version and that's what caused the corruption initially.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Steeltown
Crewman Steeltown
Crewman

Posted: ‎2025-05-06 05:46 AM

0 Likes
2
1410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 05:46 AM

Attached is a screenshot of the error message I get now when trying to access the UPS's web/GUI management page in a browser.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-05-06 10:41 AM

In response to Steeltown
0 Likes
1
1399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 10:41 AM

Based only on the information you have provided it sounds like you installed the wrong NMC firmware version.

 

Depending upon when the unit was produced / purchased the system could have had a NMC 2 vs NMC 3.

 

The 2.5.X.X branch is for the current NMC 3. The 7.X.X branch is for the legacy end of life NMC 2.

 

You’ll need to identify which embedded NMC is on board the unit. Worst case you can try uploading the latest NMC 2 7.2.0 firmware branch and report back the results.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Steeltown
Crewman Steeltown
Crewman

Posted: ‎2025-05-06 01:02 PM

In response to Teken
0 Likes
0
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 01:02 PM

Solved the issue by

SSH into NMC

Enabling ftp on NMC

Using ftp to put

apc_hw21_su_2-5-4-4.nmc3

onto the ON-1571 NMC.  After rebooting the NMC, I was then able to successfully run the v2.5.4.4 Firmware Update Utility.  The key is that this model ON-1571 NMC is only compatible with _su_ firmware.  I had tried to upgrade to a _sucan_ version and that's what caused the corruption initially.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore