Re: Critical - Battery power too low to support load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Critical - Battery power too low to support load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:23 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
6
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:23 AM . Last Modified: ‎2024-03-12 03:06 AM

Re: Critical - Battery power too low to support load

Hello

I have a very similar problem with some of my SURT10000 units. I've replaced the batteries with all new ones. On performing a self test, the battery charge level indicator reduces to 0 and the management card send out messages that the Batteries are discharged. When showing as fully charged, the run time is showing as 7 minutes on 42% load. A run-time calibration also results in an immediately discharged battery and an error message.

I'm thinking that the battery charge parameter mentioned here and elsewhere may need to be reset (or the UPS itself is faulty), but I don't know how to access the interface to do that on the SURT10000 or what the correct value is.

Any help would be gratefully received.

Tom

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

You just need to go to "Inbox" when you go to forums.apc.com and you should see it in there and see an option to reply.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

Can you verify what your low battery duration is set to? This would be inside the Network Management Card interface of your UPS. That is the first step - confirming what this value is in addition to what you already provide regarding load and reported runtime.

Alternatively, you can provide me the event.txt, data.txt, and config.ini using these instructions (How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...) and I'll see the value there too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
0
1352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

Hello Angela,

It's set to 2 minutes. I think the fact that the batteries seem to discharge in seconds suggests there is something wrong.

Thanks

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
0
1352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

Hi Tom,

You can have it report "batteries discharged" when they really are not truly discharged or not charging. That is not typically reported with the 0% charge but it still could be. You haven't tried to put the UPS on battery at all yet, have you? To see if the UPS supports the load?

I think before I have you do anything, we'd really need to see the event/data log so I can see how that charge % fluctuates - I was curious is it 100-0-back to 100 immediately or is it a gradual discharge?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
0
1352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

Hello Angela,

Well, I've tried a self test and a run-time calibration. The battery charge indicator falls to 0% within a couple of minutes.

Recharging (battery indicator returning to 100%) takes a couple of hours.

Excerpt from data.txt

18-Jun-14   18:08:46    241.9   243.3   230.4   14.85   40.049.96   100.0   216.0   33.634.035.5      
18-Jun-14   17:58:46    241.9   243.3   230.4   14.98   41.049.96   100.0   216.0   33.634.035.0      
18-Jun-14   17:48:46    241.9   243.3   230.4   15.25   40.049.97   100.0   216.0   33.633.036.0      
18-Jun-14   17:38:46    243.3   243.3   231.6   14.58   40.049.94   100.0   216.0   33.634.035.5      
18-Jun-14   17:28:46    243.3   243.3   230.4   14.71   40.049.99   100.0   216.0   33.633.036.0      
18-Jun-14   17:18:46    243.3   243.3   230.4   14.85   39.049.92   100.0   216.0   33.634.035.5      
18-Jun-14   17:08:46    241.9   243.3   230.4   15.52   42.050.00   100.0   216.0   33.635.036.0      
18-Jun-14   16:58:46    240.4   241.9   230.4   14.71   40.049.97   100.0   216.0   33.634.036.0      
18-Jun-14   16:48:45    241.9   244.8   230.4   14.85   40.049.99   100.0   216.0   33.633.036.0      
18-Jun-14   16:38:45    243.3   244.8   230.4   14.58   40.049.95   100.0   216.0   33.633.035.0      
18-Jun-14   16:28:45    243.3   244.8   231.6   14.71   40.049.95   97.0216.0   33.633.035.0      
18-Jun-14   16:18:45    243.3   244.8   230.4   15.12   41.049.97   91.0216.0   33.635.036.0      
18-Jun-14   16:08:45    243.3   243.3   230.4   15.12   41.050.02   84.0216.0   33.635.035.0      
18-Jun-14   15:58:45    243.3   243.3   230.4   14.98   41.049.95   76.0216.0   33.634.034.0      
18-Jun-14   15:48:45    243.3   243.3   230.4   14.85   41.049.97   70.0216.0   33.633.034.0      
18-Jun-14   15:38:45    243.3   243.3   230.4   14.71   40.049.99   63.0216.0   33.633.034.0      
18-Jun-14   15:28:45    243.3   243.3   230.4   14.85   40.049.99   55.0216.0   33.633.034.0      
18-Jun-14   15:18:45    243.3   243.3   230.4   14.58   38.049.95   49.0216.0   33.634.034.0      
18-Jun-14   15:08:45    243.3   243.3   230.4   14.85   38.049.96   41.0216.0   33.633.035.0      
18-Jun-14   14:58:45    243.3   243.3   230.4   15.12   40.050.07   34.0216.0   33.634.033.5      
18-Jun-14   14:48:45    243.3   243.3   230.4   14.71   39.050.04   28.0216.0   33.634.033.5      
18-Jun-14   14:38:45    243.3   243.3   230.4   14.71   38.050.02   20.0216.0   33.633.033.5      
18-Jun-14   14:28:45    243.3   243.3   230.4   14.98   40.049.99   13.0216.0   33.634.033.5      
18-Jun-14   14:18:45    243.3   243.3   230.4   14.71   40.050.00   6.0 216.0   33.633.034.0      
18-Jun-14   14:08:45    241.9   243.3   230.4   14.71   39.050.04   100.0   214.9   33.633.034.5      
18-Jun-14   13:58:45    243.3   243.3   230.4   14.85   39.050.05   100.0   216.0   33.633.033.5      
18-Jun-14   13:48:45    243.3   243.3   230.4   15.12   39.050.02   100.0   216.0   33.634.033.5      
18-Jun-14   13:38:45    241.9   243.3   230.4   14.44   40.050.04   100.0   216.0   33.633.034.0      

19-Jun-14   04:33:43    UPS: A discharged battery condition no longer exists.   0x0108
19-Jun-14   04:33:38    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   22:00:14    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   21:59:59    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   21:35:17    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   21:34:32    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   21:33:57    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   21:32:50    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   21:09:24    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   21:09:05    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   21:00:11    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   20:58:38    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   20:33:34    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   20:31:12    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   20:30:50    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   20:28:28    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   20:08:59    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   20:06:12    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   19:34:50    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   19:34:10    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   19:33:15    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   19:32:58    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   19:27:54    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   19:27:25    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   18:22:33    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   18:22:08    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   17:12:45    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   17:11:45    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   17:11:03    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   17:05:43    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   16:34:06    System: Web user 'apc' logged out from 172.16.255.170.  0x001F
18-Jun-14   16:26:05    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   16:01:16    System: Web user 'apc' logged in from 172.16.255.170.   0x0015
18-Jun-14   15:54:49    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:43:37    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:42:56    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:42:21    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:41:57    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:41:46    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:41:37    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:40:29    System: Web user 'apc' logged out from 172.16.255.170.  0x001F
18-Jun-14   15:39:12    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:37:26    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:37:23    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:37:21    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:35:47    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:32:59    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:31:48    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:31:22    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:29:43    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:29:40    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:28:50    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:27:28    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:27:16    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:26:57    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:25:53    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:24:32    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:23:46    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:22:59    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:22:08    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:21:28    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   15:16:18    System: Web user 'apc' logged in from 172.16.255.170.   0x0015
18-Jun-14   15:13:44    UPS: A discharged battery condition no longer exists.   0x0108
18-Jun-14   15:05:46    System: Web user 'apc' logged out from 172.16.255.170.  0x001F
18-Jun-14   15:00:25    System: Configuration change. System inactivity timeout.    0x0033
18-Jun-14   14:59:31    System: Web user 'apc' logged in from 172.16.255.170.   0x0015
18-Jun-14   14:27:29    System: Web user 'apc' logged out from 172.16.255.170.  0x001F
18-Jun-14   14:22:00    System: Web user 'apc' logged in from 172.16.255.170.   0x0015
18-Jun-14   14:16:57    System: Web user 'apc' logged out from 172.16.255.170.  0x001F
18-Jun-14   14:11:26    UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.   0x0107
18-Jun-14   14:10:18    System: Web user 'apc' logged in from 172.16.255.170.   0x0015


Excerpt from event.txt





Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
0
1352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

Hello Angela,

Thanks for the PM. A reply to your email has bounced. How can I reply?

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

0 Likes
0
1351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:24 AM . Last Modified: ‎2024-03-12 03:06 AM

You just need to go to "Inbox" when you go to forums.apc.com and you should see it in there and see an option to reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore