APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:22 PM . Last Modified: 2024-03-19 03:38 AM
If you weren't aware of it from reading all the air distribution white papers on cooling, you SHOULD know that all that air coming up into the bottom of computer racks through those big cable cut out holes in the raised floor is robbing pressure from the perforated tiles in the front of the racks and that air come up into the bottom of the rack is counterproductive. Add that to the problem of keeping floor tile cut trim installed on a floor tile, and underfloor cable jackets getting cut by the sharp edges of the tile cuts and you have a single solution for multiple problems.
Here's an illustration of cable brush strip used for this purpose. This brush strip includes a EDPM layer sandwiched between two rows of Nylon fiber. The layer serves two purposes 1) additional air seal and 2) helps to center the cables, taking some pressure off the fibers.
8 foot lengths of brush and holder with the extra seal is G680CLA50FS.020 for
$ 95.73 from 804-743-0982 Danielle Fernandez X212
www.sealeze.com
You can install this with a hacksaw, a pair of pliers to crimp the brush strip after you cut it, and a screw gun to screw it to the floor tile. The brush section is 4.5" from the edge of the tile cut to the end of the brush. I've been working with this manufacturer for a molded FLEXIBLE option of this also, which is due out in June 07. So you can install it with a carpet knife and a screw gun.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:22 PM . Last Modified: 2024-03-19 03:38 AM
If you weren't aware of it from reading all the air distribution white papers on cooling, you SHOULD know that all that air coming up into the bottom of computer racks through those big cable cut out holes in the raised floor is robbing pressure from the perforated tiles in the front of the racks and that air come up into the bottom of the rack is counterproductive. Add that to the problem of keeping floor tile cut trim installed on a floor tile, and underfloor cable jackets getting cut by the sharp edges of the tile cuts and you have a single solution for multiple problems.
Here's an illustration of cable brush strip used for this purpose. This brush strip includes a EDPM layer sandwiched between two rows of Nylon fiber. The layer serves two purposes 1) additional air seal and 2) helps to center the cables, taking some pressure off the fibers.
8 foot lengths of brush and holder with the extra seal is G680CLA50FS.020 for
$ 95.73 from 804-743-0982 Danielle Fernandez X212
www.sealeze.com
You can install this with a hacksaw, a pair of pliers to crimp the brush strip after you cut it, and a screw gun to screw it to the floor tile. The brush section is 4.5" from the edge of the tile cut to the end of the brush. I've been working with this manufacturer for a molded FLEXIBLE option of this also, which is due out in June 07. So you can install it with a carpet knife and a screw gun.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:22 PM . Last Modified: 2024-03-19 03:38 AM
If you weren't aware of it from reading all the air distribution white papers on cooling, you SHOULD know that all that air coming up into the bottom of computer racks through those big cable cut out holes in the raised floor is robbing pressure from the perforated tiles in the front of the racks and that air come up into the bottom of the rack is counterproductive. Add that to the problem of keeping floor tile cut trim installed on a floor tile, and underfloor cable jackets getting cut by the sharp edges of the tile cuts and you have a single solution for multiple problems.
Here's an illustration of cable brush strip used for this purpose. This brush strip includes a EDPM layer sandwiched between two rows of Nylon fiber. The layer serves two purposes 1) additional air seal and 2) helps to center the cables, taking some pressure off the fibers.
8 foot lengths of brush and holder with the extra seal is G680CLA50FS.020 for
$ 95.73 from 804-743-0982 Danielle Fernandez X212
www.sealeze.com
You can install this with a hacksaw, a pair of pliers to crimp the brush strip after you cut it, and a screw gun to screw it to the floor tile. The brush section is 4.5" from the edge of the tile cut to the end of the brush. I've been working with this manufacturer for a molded FLEXIBLE option of this also, which is due out in June 07. So you can install it with a carpet knife and a screw gun.
Link copied. Please paste this link to share this article on your social media post.
You have two options to continue your visit.
OR