Rack PDU AP7902 - Statistics Question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Rack PDU AP7902 - Statistics Question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

0 Likes
5
1918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

Rack PDU AP7902 - Statistics Question

I am doing some budgeting and I would like to come up with some sort of cost of electricity associated with the equipment supported by our AP7902s. I can see from the UI they provide Amps, but in order to calculate something like kW hours I would need like a watt or volt measurement. Does anyone have any suggestions where/how I can get this kind of number? Has anyone had to do this before?

Thanks in advance!

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • apc
  • communication
  • management
  • pdu
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:57 AM

0 Likes
0
1919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:57 AM

For determining utility rates yes, you would want to know Kwh which at a steady state 960w instantaneous is .96kwh.


I picked a winna:... Didn't wanna bring pf into this discussion because for someone trying to get a ballpark on power usage of a small rack mount PDU they more than likely aren't breaking out a PQA to get that info. Otherwise there wouldn't be any question to how much power was being used because it would displayed on the PQA.


Note: This is just a ballpark figure and if your determining how much to charge a user then you will be safe as the actual KW load can't be any higer than Amps*Volts regardless of PF.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

0 Likes
0
1919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

I am doing some budgeting and I would like to come up with some sort of cost of electricity associated with the equipment supported by our AP7902s. I can see from the UI they provide Amps, but in order to calculate something like kW hours I would need like a watt or volt measurement. Does anyone have any suggestions where/how I can get this kind of number? Has anyone had to do this before?

Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

0 Likes
0
1919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

If I understand the way an ampere works, it is measured in coulombs per second. So using your example 8(120)=960w/s? Is that correct? It would then have to be converted to kWh right?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

0 Likes
0
1919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:58 AM

just to clarify, you would like to find out these measurements of the load attached to the PDU, correct? the AP7902 assumes a power factor of 1 and assumes the nominal input voltage that you are using. you can adjust some of these values via SNMP though so that you are able to calculate the kWh and kWh for your load. i honestly am not 100% how to do these calculations though. this may help? -> http://answers.yahoo.com/question/index?qid=20080102150302AAxmlnf

i would just like to indicate though, APC's New Next Gen PDUs do calculate all of this for you in real time and they measure current and input voltage to make these figures as accurate as possible.

you can check out this brochure on our metered rack pdus -> http://www.apcmedia.com/salestools/JKUR-87JM4Z_R1_EN.pdf

here is the brochure on the switched rack pdus, the replacement for the AP79xx series you have now -> http://www.apcmedia.com/salestools/JKUR-8ADRTQ_R1_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:57 AM

0 Likes
0
1919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:57 AM

Do you have the network interface set up? You should be able to log into the Web Browser for the specific PDU you are trying to get the info for and get a current measurement. Or read the display on the front of the PDU. You could then multiply that number by the voltage of the PDU output.

So if the PDU displayed 8A and you measured the PDU as having 120VAC. This PDU would be powering 960w of load.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:57 AM

0 Likes
0
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:59 AM . Last Modified: ‎2024-03-18 02:57 AM

For determining utility rates yes, you would want to know Kwh which at a steady state 960w instantaneous is .96kwh.


I picked a winna:... Didn't wanna bring pf into this discussion because for someone trying to get a ballpark on power usage of a small rack mount PDU they more than likely aren't breaking out a PQA to get that info. Otherwise there wouldn't be any question to how much power was being used because it would displayed on the PQA.


Note: This is just a ballpark figure and if your determining how much to charge a user then you will be safe as the actual KW load can't be any higer than Amps*Volts regardless of PF.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore