RC502+RP502 integeration vs only RP502

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • RC502+RP502 integeration vs only RP502
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
4
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

RC502+RP502 integeration vs only RP502

Hi,

We have designed HACS with 6 units ACRP502 inrow.
In order to reduce prices and elect bill but not at the expense of reducing performance, can below be correct:

6 x ACRP502 = (2 x ACRP502) + (4 x ACRC502)

i.e. can (2 x ACRP502) + (4 x ACRC502) be implemented instead of 6 x ACRP502 without losing any cooling & humidity control performance ?

It is a concern we will be losing much more in performance in future. Please can someone help with more detail look at above suggestion.

Thanks

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

Hi,

We have designed HACS with 6 units ACRP502 inrow.
In order to reduce prices and elect bill but not at the expense of reducing performance, can below be correct:

6 x ACRP502 = (2 x ACRP502) + (4 x ACRC502)

i.e. can (2 x ACRP502) + (4 x ACRC502) be implemented instead of 6 x ACRP502 without losing any cooling & humidity control performance ?

It is a concern we will be losing much more in performance in future. Please can someone help with more detail look at above suggestion.

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

The question of can 2 RP and 4 RC be used in a HACS is yes they can. Will 2 RP 4 RC provide the same level of cooling and humidity control as 6 RP is no. RC's don't provide any humidity control. Both the RC and RP are both rated for 43kw cooling capacity.

However you could probobly get away with only using 2 RP's and 4 RC's as I doubt you would need the full level of humidity control that 6 RP's would provide in a HACS of this size. Is there any additional means of humidity control in your data center? Have you had an engineer determine the amount of humidification needed for your climate and building? That would be the first step to determine if only 2 RP's will be sufficient in your datacenter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

Thank you for your answer.
Climate control has been determined by an engineer and having 2RP+6RC is his suggestion, therefore you are correct 2RP will be enough for the HACS humidity control but the suggestion is mainly for the reason of having even more power efficiencies in our HACS since RP power consumption due to its humidification characteristic is much more than RC. is this true?

In the case of 2RP doing the job of humidity control, is power efficiency of 2RP+4RC better than 6RP ? or is it equal ?
will there be a waste of power having 6RP controlling humidity when 2RP will be enough or no difference due to systems' control set up?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

The answer of efficiency is a bit hard to determine from RC to RP but RC's can only consume a set amount of power at max load where a RP can consume RC max power plus any power needed for de/humidification. The RP has a higher power consumption rating due to the humidification circuit and the reheat coils which are used during dehumidification. During normal operation with no humidification or dehumidification demand the RC and RP would use nearly the same amount of power to provide the same level of cooling.

If you were to use the 6 RP's would you group them together? If so then having 6 RPs would provide no greater dehumidification control than 2 because the Master unit will only allow 1 unit at a time to enter dehumidification mode. Typically cooling units with a high load are grouped together in a HAC to provide even cooling and to prevent hot spots. So for the greatest efficiency you would be best to group your 4 RC's together and have your 2 RP's grouped together.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:27 AM . Last Modified: ‎2024-03-18 03:32 AM

Hi,

We have designed HACS with 6 units ACRP502 inrow.
In order to reduce prices and elect bill but not at the expense of reducing performance, can below be correct:

6 x ACRP502 = (2 x ACRP502) + (4 x ACRC502)

i.e. can (2 x ACRP502) + (4 x ACRC502) be implemented instead of 6 x ACRP502 without losing any cooling & humidity control performance ?

It is a concern we will be losing much more in performance in future. Please can someone help with more detail look at above suggestion.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore