Powerchute Network problem on NMC registration
Hi,
I have a Smart UPS C1500IC (SmartConnect). I wanted to test PowerChute during a DRP/BCP test. So, I connected the UPS via ethernet (it gets an IP address) and installed PowerChute on a VM. It connects properly to vCenter, and then it asks for a username/password/authentication phrase. I'm not sure if this corresponds to something existing, so I just enter anything. Then, it asks for the IP of the UPS, which I provide. But it says, 'Error registering with the Network Management Card(s).' without any log. What should I do to make it work?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-0106:42 AM
For the PowerChute Virtual Machine and Linux systems, see: "Error registering with the Network Management Card when running the PowerChute Virtual Machine or on a Linux system.pdf."
For PowerChute running on a Windows system, see: "Error registering with the Network Management Card when running the PowerChute on a Windows System.pdf."