PowerChute on Windows PC failing to action Maintenance Mode on ESXi Hosts.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute on Windows PC failing to action Maintenance Mode on ESXi Hosts.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
CBT
Crewman CBT
Crewman

Posted: ‎2022-03-19 04:09 AM . Last Modified: ‎2022-03-19 05:18 AM

1 Like
2
1926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-19 04:09 AM . Last Modified: ‎2022-03-19 05:18 AM

PowerChute on Windows PC failing to action Maintenance Mode on ESXi Hosts.

Greetings,

 

I have several issues with PowerChute configuration/setup.

 

My environment is configured as follows:

 

1 x Windows PC with PowerChute Network Shutdown installed & configured to LAN.

2 x Dell Poweredge R430 (installed withe ESXi 7 Hosts & vCenter Server Appliance VM + Multiple Guest VMs).

1 x APC Smart UPS with Network Management Card.

1 x Synology RS815RP+ NAS

 

 

1. Shutdown sequence of Group 1 & Group 2 are inverted (Group 1 - 192.168.1.247 shutdown command initiated first instead of Group 2 192.168.1.249 first).

 

2. All VMs shutdown including vCenter Server Appliance VM but fails to initiate 'Maintenance Mode' on the ESXi Hosts.

 

I see from the event log 'Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.' this would be due to the VM shutdown commands have already been initiated, the commands i want to issue are for the final shutdown of the ESXi Hosts and assume a scripted file command should be sent direct to via their I.P Address's and NOT via the vCenter Server Appliance which has already been initiated shutdown?

 

3. Cannot find any instructions on the internet for issuing either a .cmd file or 'SSH' command to shutdown the ESXi Hosts.

 

Here is the Event Log...

 

03/19/2022 10:10:20 UPS Outlet Group has turned on.
03/19/2022 10:06:06 ERROR: The ini file is missing shutdownCommandFile key from section Shutdown.
03/19/2022 10:06:06 ERROR: The ini file is missing shutdownCommandFile key from section Shutdown.
03/19/2022 10:05:17 Available runtime has been exceeded.
03/19/2022 10:05:17 Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.
03/19/2022 10:05:10 Outlet Group Outlet Group 1 is turned off for NMC 192.168.1.239.
03/19/2022 10:05:09 PowerChute successfully accessed TCP port 6547.
03/19/2022 10:05:09 PowerChute is attempting to access TCP port 6547.
03/19/2022 10:05:09 PowerChute Network Shutdown version 4.4.1 monitoring started.
03/19/2022 10:05:07 UPS Outlet Group has turned off.
03/19/2022 10:05:07 Communication has been established.
03/19/2022 10:05:07 PowerChute successfully accessed UDP port 3052.
03/19/2022 10:05:07 PowerChute is attempting to access UDP port 3052.
03/19/2022 09:41:35 Shutting down physical machine that PowerChute is running on.
03/19/2022 09:41:13 Shutdown Host unsuccessful for Host 192.168.1.249.
03/19/2022 09:40:43 Shutdown Host unsuccessful for Host 192.168.1.247.
03/19/2022 09:38:27 Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.
03/19/2022 09:38:07 Shutting down vCenter Server VM vCenterServer.
03/19/2022 09:36:03 Shutting down VMs on Host 192.168.1.249.
03/19/2022 09:35:51 UPS critical event: Outlet Group Turn off initiated.
03/19/2022 09:35:51 UPS Outlet Group: Outlet Group 1 turn off has been initiated.
03/19/2022 09:35:47 No vApp to shutdown on Host 192.168.1.247.
03/19/2022 09:35:47 Starting vApp shutdown process.
03/19/2022 09:35:47 Shutting down VMs on Host 192.168.1.247.
03/19/2022 09:35:46 PowerChute is turning off UPS 192.168.1.239
03/19/2022 09:35:46 Shutdown sequence started on Hosts 192.168.1.247, 192.168.1.249 in response to UPS critical event: On Battery.
03/19/2022 09:35:46 UPS critical event: On Battery.
03/19/2022 09:35:26 UPS has switched to battery power.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-03-23 12:46 PM

1 Like
1
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-23 12:46 PM

@CBT 

 

Do you have vCLS enable? If so see Schneider Electric FAQ https://www.apc.com/us/en/faqs/FA416409/

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CBT
Crewman CBT
Crewman

Posted: ‎2022-03-23 02:53 PM

In response to BillP
0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-23 02:53 PM

Thanks for the response.

 

I tried that method a couple of days back, followed all the instructions and it still failed to shutdown the hosts,

 

I found a method of disabling both the vCLS VMs though the VCSA config file which completely removes them. The shutdown still fails, i'm just analyzing the pcnsconfig.ini and log files to see whats going wrong.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore