Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

PowerChute is not receiving data from the Network Management Card

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute is not receiving data from the Network Management Card
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

0 Likes
2
3311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

PowerChute is not receiving data from the Network Management Card

Hello

I'm having some problems linking Powerchute Network Shutdown with my UPS (NMC 9631 v6.8)

I installed PNS 4.4 on a Raspberry Pi 3 (It's a Debian ARM distro). I simply replaced the JRE binaries packed in the installer, with JRE from Oracle for ARM architecture

PNS and NMC are in different subnets (a VPN site2site is enstablished between these subnets). all type of traffic between these two subnets is permitted in any direction.

PNS: 172.16.1.254:6547

NMC: 192.168.250.201:80

I set up Passphrase correctly and PNS registers itself in the NMC client list.

This is the error

BwF0B6nb6RrDR2ZnOyneZQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngBwF0B6nb6RrDR2ZnOyneZQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

 

As suggested in other topics I have tried to monitor traffic flowing through my firewall and I see NMC's reply to dest port 3052 UDP

Fi13oIo1Lwzne69FyE%2F%2FCg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngFi13oIo1Lwzne69FyE%2F%2FCg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

 

I can't packet-trace where the PNS is installed but I'm sure there is no firewall installed. And I see sockets correctly binded

Ure5oySr2KuXt7vut9NKzw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngUre5oySr2KuXt7vut9NKzw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

I have no clue...

Can you help me? thanks!

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 9631
  • network_management_card
  • powerchute_network_shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

0 Likes
0
3308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

Indeed, it was a network problem, an access list was blocking traffic initiating from the UPS, but not traffic comin back for a previous connection (NMC really starts a *new* connection to port 3052)

Unfortunately I had to uninstall it because, once configured,  there was no option to integrate in vmware.

So i downloaded the PNS for Virtualization .ova file and deployed in my single esxi host.

I have some trouble to understand how it works but I think I'll work it out...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

0 Likes
0
3308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

Hi Paolo,

You have a whole lot of moving parts here so I can't guarantee that this will work.

First thing to check is if powerchute is enabled on the NMC from FW6.8.2 onward it is not enabled by default.

Next thing to check would be is HTTP/HTTPS enabled on the NMC?

If the NMC is right then more than likely your issue is network related, I'm not going to comment on the fact your running it on ARM but I would say that if it was that easy I'd imagine it would already have been done.

-Gavan 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

0 Likes
0
3309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:38 AM

Indeed, it was a network problem, an access list was blocking traffic initiating from the UPS, but not traffic comin back for a previous connection (NMC really starts a *new* connection to port 3052)

Unfortunately I had to uninstall it because, once configured,  there was no option to integrate in vmware.

So i downloaded the PNS for Virtualization .ova file and deployed in my single esxi host.

I have some trouble to understand how it works but I think I'll work it out...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore