PowerChute Network Shutdown - What I'm doing wrong?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown - What I'm doing wrong?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
11
9655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

PowerChute Network Shutdown - What I'm doing wrong?

Hello everybody,

I have troubles with the proper configuration of the network shutdown.

Summary:

1 Smart-UPS 1000

1 single host with ESXi 6.0.0

2 Virtual Windows Server 2012 R2

1 Virtual PowerChute Network shutdown from here: http://www.apc.com/us/en/tools/download/index.cfm

apc user is administrator and set in the ESXi.

Startup/Shutdown by the VMs is set to Shutdown Guests with 60 seconds delay.

the UPS is connected with the Virtual PowerChute network shutdown.

And still by tests with power down the servers didn't shutdown properly. Every time there is an error about Kernel Power (Event ID 41) and "computer didn't shutdown properly".

What I'm doing wrong?

I'm not sure also how exactly the process is running. For example in case of power down what is the sequence?

UPS -> Management Card -> VM Network Shutdown -> ESXi -> VMs

or

UPS -> Management Card -> VM Network Shutdown -> UPS -> ESXi -> VMs 

 

the current settings are:

by PowerChute Network Shutdown:

Shutdown settings - Turn off the UPS

Configure Events - Shutdown by Runtime exceeded

PowerChute Network Shutdown -> UPS Configuration -> Powerchute Agents -> VM PowerChute

by the UPS:

Shutdown: 8 minutes

Shutdown delay: 360 seconds

PowerChute configuration: Maximum required Delay 8 minutes

PowerChute clients: VM Powerchute

When I have PowerChute section on the UPS, do I really need the VM Network shutdown? Should I actually add as a client the ESXi instead of the VM PowerChute Network shutdown?

Thanks in advance

Edit:

remaining time on the UPS shows 28 minutes. This should be sufficient because we don't have longer than 10 minutes powerdowns.

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • configuration
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

ok, Bill. Thank you very much for the information and help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi,

You should read the PowerChute Network Shutdown VMware User's Guide, and Application Note 180. 

PowerChute Network Shutdown version 4.2 offers 3 installation options when dealing with VMware ESXi. You can install on a Windows server (not a VM must be a physical server), you can install PowerChute on VMware vMA, or you can install PowerChute Network Shutdown virtual appliance. each of these option allow you to configure PCNS to shutdown a single ESXi host or work with VMware vCenter Server to power down multiple hosts. 

the shutdown process for a single ESXi host is

1. NMC reports that the UPS is on battery.
2. Shutdown delay for the On Battery event elapses.
3. PowerChute sends power down signal to ESXi host and if configured to do so will send power down signal to UPS
4. ESXi host commands the VMs down based on the settings in Virtual Machine Startup/Shutdown See Schneider Electric FAQ FA159688
5. ESXi host powers down

NOTE: PowerChute can only power down a ESXi host that has a VMware Standard, Enterprise, Enterprise Plus License. It cannot power down a system that is running on the free VMware license. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi Bill,

thank you for your answer but it is still unclear to me. I've checked the links and documentation from you but there is not much information about single esxi host and settings. I've already installed the Virtual solution (you could see it in my description)

For example:

which agent should be in the list of PowerChute Network Shutdown - the Virtual Appliance or the ESXi host

is the time which I've set already is enough or proper set?

when I have already in NMC a powerchute settings do I need an additional Virtual Appliance or physical computer.

which "client" should I set there - the esxi or the ups?

thanks in advance

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi,

On 5/29/2017 5:44 AM, Boris said:

which agent should be in the list of PowerChute Network Shutdown - the Virtual Appliance or the ESXi host

When runnning PowerChute Setup you should enter the ip address or host name of the ESXi host to be shutdown.

On 5/29/2017 5:44 AM, Boris said:

is the time which I've set already is enough or proper set?

I cannot say because I do not know how much time your VMs need to power down. My recommendation is not to use Runtime Exceeded as the shut down. I suggest configuring Runtime Remaining Below Threshold and set that to 720 seconds (12 minutes). This way when the UPS falls below 12 minutes of available runtime the shutdown process will be started. This recommendation is based on you writing that the system does not need greater that 10 minutes to power down. I added an extra 2 minutes for saftey. 

On 5/29/2017 5:44 AM, Boris said:

when I have already in NMC a powerchute settings do I need an additional Virtual Appliance or physical computer.

which "client" should I set there - the esxi or the ups?

The PowerChute client display on the NMC should be the IP address of the PowerChute appliance you installed on the ESXi host. 

In the example above my PowerChute Appliance has been added as 10.218.45.248 and is associated with Outlet Group 3 on a SMX1500. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi Bill,

I've checked my configuration and made the change for the threshold. I've made also a couple of screenshots to show you.

Virtual Appliance

 

Virtual Appliance 2

 

Virtual Appliance 2

 

 

here in the screenshots 10.6.170.10 is the IP of the NMC and 10.6.168.11 the Virtual Appliance.

Unfortunately I can't see "PowerChute Network Shutdown Clients Configuration" by me in the menu.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi,

On 6/1/2017 8:42 AM, Boris said:

Unfortunately I can't see "PowerChute Network Shutdown Clients Configuration" by me in the menu.

What menu are you referring to? the PowerChute Network Shutdown Client configuration is accessed at https://10.6.168.11:6547 it is not access through the NMC. The NMC only list the PCNS clients that have been registered with it. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Exactly, that's why I posted the screenshot from the menu by Virtual Appliance (https://10.6.168.11:6547)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi,

I sorry but I do not understand. What are your expectations and what do you think is missing?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

I think that by me is missing in the Virtual appliance this menu "PowerChute Network Shutdown Clients Configuration"

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi Bill,

do you know why this menu could me missing by me? Is it a problem of the PowerChute Virtual Appliance version or it could be something else?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

Hi,

There is no PCNS Virtual Appliance Client Shutdown menu. The client shuts itself down after commanding the host to power down and start up when the host starts up. 

These are the menu options

and these are the shutdown settings

For assistance with VM shutdown and start up see Schneider Electric FAQ http://www.apc.com/us/en/faqs/FA159688/

Also note that PCNS can only shutdown fully licensed versions of VMware ESXi host. The licenses that are acceptable are VMware Standard, Enterprise, Enterprise Plus http://www.vmware.com/products/vsphere/pricing

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

0 Likes
0
9651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:11 AM . Last Modified: ‎2024-02-29 10:15 PM

ok, Bill. Thank you very much for the information and help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore