Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi, We have a galaxy 5000 80KVA UPS.
Our UPS alarm is "Power supply board fuse blown". I pressed help key and information was "The DC power supply fuse has blown".
When I closed Q1 (input mains) charger was starting and DC bus was 800V DC.
We tested all of fuses and micro switches on the UPS but them were OK, then we replaced ALIN, DALIN and DCHON boards but alarm is present.
Where is problem? Please guide us.
Regards,
Tohidi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi again,
I asked your regional support and they told me:
That issue should come from supply board. But as they already replaced it, to go further in the analysis, we need the UPS tuner logs. So I'm afraid customer will have to call local Schneider Services.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi Tohidi,
Unfortuantely we don't have the expertise here to support this type of issue for this UPS. For the quickest service, I recommend you call/email your local technical support office (http://www.apc.com/site/support/index.cfm/contact-information/). Otherwise, that is what I'll have to do myself and it could take several days to get an answer, which for this type of UPS is the same as what I've just told you anyway due to its complexity. It also may require a service technician.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi Angela,
I will be grateful if you support us and get an answer. We will wait several days.
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi again,
I asked your regional support and they told me:
That issue should come from supply board. But as they already replaced it, to go further in the analysis, we need the UPS tuner logs. So I'm afraid customer will have to call local Schneider Services.