Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi, We have a galaxy 5000 80KVA UPS.
Our UPS alarm is "Power supply board fuse blown". I pressed help key and information was "The DC power supply fuse has blown".
When I closed Q1 (input mains) charger was starting and DC bus was 800V DC.
We tested all of fuses and micro switches on the UPS but them were OK, then we replaced ALIN, DALIN and DCHON boards but alarm is present.
Where is problem? Please guide us.
Regards,
Tohidi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi again,
I asked your regional support and they told me:
That issue should come from supply board. But as they already replaced it, to go further in the analysis, we need the UPS tuner logs. So I'm afraid customer will have to call local Schneider Services.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi Tohidi,
Unfortuantely we don't have the expertise here to support this type of issue for this UPS. For the quickest service, I recommend you call/email your local technical support office (http://www.apc.com/site/support/index.cfm/contact-information/). Otherwise, that is what I'll have to do myself and it could take several days to get an answer, which for this type of UPS is the same as what I've just told you anyway due to its complexity. It also may require a service technician.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi Angela,
I will be grateful if you support us and get an answer. We will wait several days.
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi again,
I asked your regional support and they told me:
That issue should come from supply board. But as they already replaced it, to go further in the analysis, we need the UPS tuner logs. So I'm afraid customer will have to call local Schneider Services.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.