Power restored before full shutdown - Best way to calculate & reduce host shutdown times?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power restored before full shutdown - Best way to calculate & reduce host shutdown times?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:54 AM . Last Modified: ‎2024-03-19 02:42 AM

0 Likes
3
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:54 AM . Last Modified: ‎2024-03-19 02:42 AM

Power restored before full shutdown - Best way to calculate & reduce host shutdown times?

We ran a test that demonstrated a graceful shutdown of all VMs within the target timeframe. Unfortunately, it took another 15+ minutes before the hosts powered down, and power was restored in that period.

1.  The vCenter log shows the first host getting a shutdown trigger at least 15 minutes after power was restored. Is there a way to abort the host shutdown during the waiting period, or signal just to shut down the VMs but not the ESXi hosts?

2. Is there a non-obvious setting that has the host delay set so far out from VM shutdowns?

Labels
  • Labels:
  • General Questions & Suggestions
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:55 AM . Last Modified: ‎2024-03-19 02:42 AM

0 Likes
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:55 AM . Last Modified: ‎2024-03-19 02:42 AM

Hi,

On 10/22/2019 3:03 PM, John said:

I'm not sure of how to access the pcnsconfig.ini - I assume that's on the "PowerChute Network Shutdown 4.1 for VMware" virtual appliance. I can see that in vSphere Client along with the VMs on that host in the cluster: what's the best way to access it? 

You can open the VM in vShpere client, VSphere web client, or using an SSH program. I user the web client and SSH. The .ini file will be found in /opt/APC/PowerChute/group1

I recommend you upgrade to PCNS 4.3 as there have been many improvements made since 4.1. 

On 10/22/2019 3:03 PM, John said:

We want to add a command file to execute: from what I've seen in earlier responses (saw a few of yours, from 2018), the file will have to be placed "locally" - also on the pcns appliance?  

- I've seen that the command file can have a .cmd or .bat extension; is it a regular batch file with Windows syntax?

The file should be stored on the PCNV VM and since the VM is a Linux OS the file extension needs to be .sh. A .bat or .cmd file will not run. We have FAQ FA159559 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:54 AM . Last Modified: ‎2024-03-19 02:42 AM

0 Likes
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:54 AM . Last Modified: ‎2024-03-19 02:42 AM

Hi,

On 10/21/2019 2:05 PM, John said:

1.  The vCenter log shows the first host getting a shutdown trigger at least 15 minutes after power was restored. Is there a way to abort the host shutdown during the waiting period, or signal just to shut down the VMs but not the ESXi hosts?

No. The purpose of PowerChute is to power down hosts and if configured power off VMs. 

On 10/21/2019 2:05 PM, John said:

2. Is there a non-obvious setting that has the host delay set so far out from VM shutdowns?

The basic shutdown is, VM Migration, VMs/vApps shutdown, vCenter Server shutdown, Hosts shutdown. PCNS will wait the delay for migration, then power off VM delay, wait the delay for vCenter Server to power off, and finally power off hosts. 

The shutdown process is listed in Application Note 180. You will find the setting in the GUI or you can edit the setting in pcnsconfig.ini

[HostConfigSettings]
VMware_connect_timeout = 10
VMware_read_timeout = 15
vm_prioritization_enabled = false
delay_after_exit_maintenance_mode = 30
delay_after_vcsa_powered_on_and_connected = 30
enable_guest_vm_migration = true
guest_vm_migration_duration = 120
enable_custom_target_vm_migration = false
custom_target_hosts =
enable_guest_vm_vapp_shutdown = true
guest_vm_vapp_shutdown_duration = 120
enable_guest_vm_vapp_startup = true
guest_vm_vapp_startup_duration = 120
vm_startup_delay_duration = 0
force_VApp_shutdown = true
delay_maintenance_mode = true
delay_maintenance_mode_timeout = 15
vm_startup_rescan_hba_duration = 15
enable_plugin = false
plugin_type =
startup_waits_for_all_hosts_online = true
VCSA_shutdown_duration = 240
hostlist = 10.0.0.20|10.0.0.21|10.0.0.22

 

[VMPrioritization]
vm_list_high =
vm_list_medium =
vm_list_low =
vm_list_group_1 =
vm_list_group_2 =
vm_shutdown_duration_high = 0
vm_shutdown_duration_medium = 0
vm_shutdown_duration_low = 0
vm_shutdown_duration_group_1 = 0
vm_shutdown_duration_group_2 = 0
vm_shutdown_duration_none = 0
vm_migration_duration_high = 0
vm_migration_duration_medium = 0
vm_migration_duration_low = 0
vm_migration_duration_group_1 = 0
vm_migration_duration_group_2 = 0
vm_migration_duration_none = 0
vm_startup_duration_high = 0
vm_startup_duration_medium = 0
vm_startup_duration_low = 0
vm_startup_duration_group_1 = 0
vm_startup_duration_group_2 = 0
vm_startup_duration_none = 0

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:55 AM . Last Modified: ‎2024-03-19 02:42 AM

0 Likes
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:55 AM . Last Modified: ‎2024-03-19 02:42 AM

Thanks, Bill. That was clear & helpful.

I'm not sure of how to access the pcnsconfig.ini - I assume that's on the "PowerChute Network Shutdown 4.1 for VMware" virtual appliance. I can see that in vSphere Client along with the VMs on that host in the cluster: what's the best way to access it? 

We want to add a command file to execute: from what I've seen in earlier responses (saw a few of yours, from 2018), the file will have to be placed "locally" - also on the pcns appliance?  

- I've seen that the command file can have a .cmd or .bat extension; is it a regular batch file with Windows syntax?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:55 AM . Last Modified: ‎2024-03-19 02:42 AM

0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:55 AM . Last Modified: ‎2024-03-19 02:42 AM

Hi,

On 10/22/2019 3:03 PM, John said:

I'm not sure of how to access the pcnsconfig.ini - I assume that's on the "PowerChute Network Shutdown 4.1 for VMware" virtual appliance. I can see that in vSphere Client along with the VMs on that host in the cluster: what's the best way to access it? 

You can open the VM in vShpere client, VSphere web client, or using an SSH program. I user the web client and SSH. The .ini file will be found in /opt/APC/PowerChute/group1

I recommend you upgrade to PCNS 4.3 as there have been many improvements made since 4.1. 

On 10/22/2019 3:03 PM, John said:

We want to add a command file to execute: from what I've seen in earlier responses (saw a few of yours, from 2018), the file will have to be placed "locally" - also on the pcns appliance?  

- I've seen that the command file can have a .cmd or .bat extension; is it a regular batch file with Windows syntax?

The file should be stored on the PCNV VM and since the VM is a Linux OS the file extension needs to be .sh. A .bat or .cmd file will not run. We have FAQ FA159559 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of