Power management multiple Apple computers with Pro 1300 / 1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power management multiple Apple computers with Pro 1300 / 1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

0 Likes
3
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

Power management multiple Apple computers with Pro 1300 / 1500

Hi,

Its very easy to manage the preferences off just one Mac with the USB cable connected to the APC.
How about a 2nd Apple computer and a Synology DS1510+ ?
Can I connect all off them via a USB splitter?
Is there a network option?

The connection on the APC looks like a Ethernet Jack. Can I connect it to my home network?

Thanks!

Rogier

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • hub
  • mac
  • manage
  • multiple
  • nas
  • network.
  • pc
  • power
  • synology
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

Hi,

I had the same problem. One UPS, 4 PC (NAS) and an iMac to control.

My solution works and has been robustly tested to shutdown MAC and PC - with a cancel option for PC (can't do it on mac once shutdown -h has been invoked)

HOW TO REMOTE SHUTDOWN ALL MACHINES (PC and MAC) ATTACHED TO AN APC UPS

To remotely shutdown any PC on the same network:

CHANGE THE FOLLOWING SETTINGS ON EACH REMOTE COMPUTER:

In CONTROL PANEL

Network and Sharing Center, Change Advanced Sharing settings

"Private" enable "Turn on File and Printer sharing"

In REGEDIT 

RUN regedit.exe

Add a new DWORD

HKEY_LOCAL_MACHINE\SOFTWARE\Microsoft\Windows\CurrentVersion\Policies\System

LocalAccountTokenFilterPolicy  DWORD:00000001

In SECPOL (Windows Pro and Enterprise ONLY)

RUN secpol.msc

Local Security Policy, Security Settings, Local Policies, User Rights Assignment

Add "Everyone" to "Force shutdown from a remote system"

Then set up the event task in TASK SCHEDULER from the PC with the UPS attached to it.

RUN taskschd.msc

TO SHUTDOWN ALL NOMINATED MACHINES

CREATE BASIC TASK

Give the TASK a NAME and a DESCRIPTION [next]

Trigger: “When a specific event is logged” [next]

When an event is logged:

LOG: Application

SOURCE: APC UPS SERVICE

EVENT ID: 174

[next]

ACTION: “Start a program” [next]

START A PROGRAM

c:\scripts\upsshutdown.bat [next]

[finish]

TO CANCEL SHUTDOWN OF ALL NOMINATED MACHINES

CREATE BASIC TASK

Give the TASK a NAME and a DESCRIPTION [next]

Trigger: “When a specific event is logged” [next]

When an event is logged:

LOG: Application

SOURCE: APC UPS SERVICE

EVENT ID: 61455

[next]

ACTION: “Start a program” [next]

START A PROGRAM

c:\scripts\upscancelshutdown.bat [next]

[finish]

BATCH FILES (to be added to c:\scripts\)

upsshutdown.bat

shutdown /s /m \\computer_name /t 120 /c “AC BLACKOUT - ORDERED SHUTDOWN IN PROGRESS”

add one line per PC you want to shutdown.

upscancelshutdown.bat

shutdown /a /m \\computer_name

add one line per PC you want to cancel the shutdown process

END OF PC METHOD

To remotely shutdown any MAC on the same network

Make sure the mac is visible on the PC with the UPS attached to it and the MAC user area is shared.

edit the ups shutdown.bat file and add the following lines for each MAC you want to shut down.

net use x: \\MAC-NAME\username

del x:\shutdown.txt

echo shutdown > x:\shutdown.txt

net use x: /delete

On each MAC

Open Automator (applications -> automator)

Choose “Folder Action” and click  “choose”

Click the “Choose folder” dialog box, select “other” and select the default user folder that corresponds to \\MAC-NAME\username and click “choose”

In “Library -> utilities” select “Run AppleScript” and drag the action into the right hand panel

replace the default AppleScript with the following:

on run {input, parameters}

 tell application "Finder"

   if exists POSIX file "/users/timstevenson/shutdown.txt" then

     say "There has been a power cut. I'm going to shutdown in one minute."

     delay 60

     tell application "System Events"

       set ProcNm_ to name of every application process whose visible is true

       repeat with i_ from 1 to count items of ProcNm_

         set TarProc_ to item i_ of ProcNm_

         try

           tell application TarProc_ to quit

         end try

       end repeat

       repeat with i_ from 1 to count items of ProcNm_

         set TarProc_ to item i_ of ProcNm_

         try

           if TarProc_ does not equal "Finder" then set app_name to TarProc_

           set the_pid to (do shell script "ps ax | grep " & (quoted form of app_name) & " | grep -v grep | awk '{print $1}'")

           if the_pid is not "" then do shell script ("kill -9 " & the_pid)

         end try

       end repeat

       tell application "finder" to shut down

     end tell

   end if

 end tell

return input

end run

SAVE the Automator file as UPSShutdown

END OF MAC METHOD

See Answer In Context

  • Tags:
  • network
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

unfortunately, this cannot be done with a Back UPS product. the data connection you see is RJ-45 but it is only a similar connection type, not a network connection.

each Back UPS can only support a single USB connection to a computer. you cannot use a USB hub or similar to attach multiple devices because you can only run one instance of software - whether you use ours or apple's native support.

to shutdown or monitor multiple devices with a single UPS, you'd need a Smart UPS product with a network management card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

Thanks for the reply, I also figured it out by experimentation.

However when I connected it to a Synology DS1512+ I did see a option in their software to set an IP address...

Something new to learn....

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

0 Likes
0
2260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:37 AM . Last Modified: ‎2024-03-06 01:31 AM

Hi,

I had the same problem. One UPS, 4 PC (NAS) and an iMac to control.

My solution works and has been robustly tested to shutdown MAC and PC - with a cancel option for PC (can't do it on mac once shutdown -h has been invoked)

HOW TO REMOTE SHUTDOWN ALL MACHINES (PC and MAC) ATTACHED TO AN APC UPS

To remotely shutdown any PC on the same network:

CHANGE THE FOLLOWING SETTINGS ON EACH REMOTE COMPUTER:

In CONTROL PANEL

Network and Sharing Center, Change Advanced Sharing settings

"Private" enable "Turn on File and Printer sharing"

In REGEDIT 

RUN regedit.exe

Add a new DWORD

HKEY_LOCAL_MACHINE\SOFTWARE\Microsoft\Windows\CurrentVersion\Policies\System

LocalAccountTokenFilterPolicy  DWORD:00000001

In SECPOL (Windows Pro and Enterprise ONLY)

RUN secpol.msc

Local Security Policy, Security Settings, Local Policies, User Rights Assignment

Add "Everyone" to "Force shutdown from a remote system"

Then set up the event task in TASK SCHEDULER from the PC with the UPS attached to it.

RUN taskschd.msc

TO SHUTDOWN ALL NOMINATED MACHINES

CREATE BASIC TASK

Give the TASK a NAME and a DESCRIPTION [next]

Trigger: “When a specific event is logged” [next]

When an event is logged:

LOG: Application

SOURCE: APC UPS SERVICE

EVENT ID: 174

[next]

ACTION: “Start a program” [next]

START A PROGRAM

c:\scripts\upsshutdown.bat [next]

[finish]

TO CANCEL SHUTDOWN OF ALL NOMINATED MACHINES

CREATE BASIC TASK

Give the TASK a NAME and a DESCRIPTION [next]

Trigger: “When a specific event is logged” [next]

When an event is logged:

LOG: Application

SOURCE: APC UPS SERVICE

EVENT ID: 61455

[next]

ACTION: “Start a program” [next]

START A PROGRAM

c:\scripts\upscancelshutdown.bat [next]

[finish]

BATCH FILES (to be added to c:\scripts\)

upsshutdown.bat

shutdown /s /m \\computer_name /t 120 /c “AC BLACKOUT - ORDERED SHUTDOWN IN PROGRESS”

add one line per PC you want to shutdown.

upscancelshutdown.bat

shutdown /a /m \\computer_name

add one line per PC you want to cancel the shutdown process

END OF PC METHOD

To remotely shutdown any MAC on the same network

Make sure the mac is visible on the PC with the UPS attached to it and the MAC user area is shared.

edit the ups shutdown.bat file and add the following lines for each MAC you want to shut down.

net use x: \\MAC-NAME\username

del x:\shutdown.txt

echo shutdown > x:\shutdown.txt

net use x: /delete

On each MAC

Open Automator (applications -> automator)

Choose “Folder Action” and click  “choose”

Click the “Choose folder” dialog box, select “other” and select the default user folder that corresponds to \\MAC-NAME\username and click “choose”

In “Library -> utilities” select “Run AppleScript” and drag the action into the right hand panel

replace the default AppleScript with the following:

on run {input, parameters}

 tell application "Finder"

   if exists POSIX file "/users/timstevenson/shutdown.txt" then

     say "There has been a power cut. I'm going to shutdown in one minute."

     delay 60

     tell application "System Events"

       set ProcNm_ to name of every application process whose visible is true

       repeat with i_ from 1 to count items of ProcNm_

         set TarProc_ to item i_ of ProcNm_

         try

           tell application TarProc_ to quit

         end try

       end repeat

       repeat with i_ from 1 to count items of ProcNm_

         set TarProc_ to item i_ of ProcNm_

         try

           if TarProc_ does not equal "Finder" then set app_name to TarProc_

           set the_pid to (do shell script "ps ax | grep " & (quoted form of app_name) & " | grep -v grep | awk '{print $1}'")

           if the_pid is not "" then do shell script ("kill -9 " & the_pid)

         end try

       end repeat

       tell application "finder" to shut down

     end tell

   end if

 end tell

return input

end run

SAVE the Automator file as UPSShutdown

END OF MAC METHOD

  • Tags:
  • network
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore