PDU amperage vs. Circuit - Please help clarify

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PDU amperage vs. Circuit - Please help clarify
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
7
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-18 03:36 AM

PDU amperage vs. Circuit - Please help clarify

Hi everyone, I've been looking around for answers but no one is able to help me so far.

We have a rack at a datacenter with a 208V/60 amp circuit coming into a 208V/60 AMP PDU and I was wondering if we lower the circuit to let say 208V/30 amp or 120/30 amp do I need to change the PDU to a 208V/30 or 120/30 as to match the amperage on the circuit?

I guess my question is if the PDU has to always match the amperage and volts of the circuit?

Thanks in advance

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • pdu
  • power
  • server
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

Hi everyone, I've been looking around for answers but no one is able to help me so far.

We have a rack at a datacenter with a 208V/60 amp circuit coming into a 208V/60 AMP PDU and I was wondering if we lower the circuit to let say 208V/30 amp or 120/30 amp do I need to change the PDU to a 208V/30 or 120/30 as to match the amperage on the circuit?

I guess my question is if the PDU has to always match the amperage and volts of the circuit?

Thanks in advance

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-18 03:36 AM

upsguy wrote:
Ideally you would want to change the supply breaker. You could probably get away with it if the PDU has overload protection built in. What model rack mount PDU do you plan on using?
I already have a 60 amp PDU but planning on lowering the 60amp breaker to 30amp.
Just a thought though, if you already have the 60A breaker and the PDU but aren't using the full amount of current you aren't wasting any power by having the larger distribution source.
I agree, but the difference in price for a 60 and 30 amp breakers are relatively high.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:20 AM . Last Modified: ‎2024-03-18 03:36 AM

If cost is an issue then why would you consider buying anything if you already have as I see it.

PDU w/60A CB -------60A cordset-------- Rackmount 60A PDU.

You only loose capacity by replacing the 60A pdu with a 30A pdu. If you don't need the 60A capacity only use 30A of it. It doesn't hurt anything to keep it at a low load level.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

upsguy wrote:
If cost is an issue then why would you consider buying anything if you already have as I see it.

PDU w/60A CB -------60A cordset-------- Rackmount 60A PDU.

You only loose capacity by replacing the 60A pdu with a 30A pdu. If you don't need the 60A capacity only use 30A of it. It doesn't hurt anything to keep it at a low load level.
If I would only get charged for what I consume then I agree with you, but this is not the case. We get billed for having 60 amp brakers on our rack no matter what the consumption is.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

I suspect you have your rack hosted at a co-location centre and they're charging you for the size of the service to your rack regardless of the actual consumption. This is an all too common tactic of many hosting sites, but, it's money for them; they charge you to install the service, then they charge a monthly rental.

If you can confirm your load is under 24 Amps (the code limit for a 30 Amp service), then you could downgrade the service to 30 Amps. The electrical service will be protected from overload by the 30 Amp breaker. While you're at it, set the warning thresholds on the PDU to correspond to the 30 Amp Service; 20 Amps for near overload, 24 Amps for overload (for example). This is not a preferred solution as it introduces the possibility of overloading the service and nuisance tripping of the breaker.

The better option would be to use a 30 Amp PDU on a 30 Amp Service.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

mfitzsimmons wrote:
I suspect you have your rack hosted at a co-location centre and they're charging you for the size of the service to your rack regardless of the actual consumption. This is an all too common tactic of many hosting sites, but, it's money for them; they charge you to install the service, then they charge a monthly rental.
Thanks for your response, you mention that this is a common tactic but what is better? to get charged for the size of the service or for consumption?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

geneticx wrote:
Thanks for your response, you mention that this is a common tactic but what is better? to get charged for the size of the service or for consumption?
It would be fair for the hosting site to charge to install the service, then charge a factor of the actual consumption. The actual load is an accurate indication of the power used, it is also an accurate indication of the load your system places on the cooling system.

What is more common is for the hosting site to charge to install the service, then also charge to rent the service monthly to cover the cost of power consumption and cooling load. In some jurisdictions it is not legal to re-sell electrical power, so this a method to get around this restriction. The problem arises when you don't use the capacity of the service. For example, a 60 Amp service at 208 Volts is rented as a 12.5 kW service and charged at something like $2,500.00 per month. The rational being that 12.5 kW is the maximum the service can supply and it takes the same amount of power to cool that load. Of course you don't use the maximum the service can provide, and, therefore do not require the maximum cooling either. This gets compounded if you have redundant electrical services. (on top of this you have your square footage charge, connection charges, management charges and so on)

This practice leads to the same issues of power consumption we see in condominium offices and residences. Since you're paying the maximum for power, why not use it. There is no incentive to upgrade to more power efficient equipment or to try to control your power consumption.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

0 Likes
0
2774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:21 AM . Last Modified: ‎2024-03-18 03:36 AM

Hi everyone, I've been looking around for answers but no one is able to help me so far.

We have a rack at a datacenter with a 208V/60 amp circuit coming into a 208V/60 AMP PDU and I was wondering if we lower the circuit to let say 208V/30 amp or 120/30 amp do I need to change the PDU to a 208V/30 or 120/30 as to match the amperage on the circuit?

I guess my question is if the PDU has to always match the amperage and volts of the circuit?

Thanks in advance

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore