Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Over frequency violation on 7723
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2511:05 PM. Last Modified: 2024-03-1903:23 AM
Over frequency violation on 7723
hi all, we are having an issue with the ats, when it goes to generator power, it shows an abnormal log includes "over frequency violation" please find the annexed log.
Date
Time
Event
03/23/2018
19:51:18
System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018
19:47:52
Automatic Transfer Switch: Event counts cleared.
03/23/2018
19:44:49
System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018
19:44:32
System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018
19:37:01
System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018
19:33:09
System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018
19:30:04
System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018
14:33:51
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018
14:33:18
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018
13:53:24
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018
13:53:15
Automatic Transfer Switch: Fault cleared on Source A.
03/23/2018
13:53:14
Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/23/2018
13:52:58
Automatic Transfer Switch: Fault exists on Source A.
03/23/2018
13:52:42
Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/23/2018
13:52:42
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018
13:39:42
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018
13:39:12
Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/23/2018
13:38:28
Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/23/2018
13:38:28
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018
13:37:33
Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/23/2018
13:36:41
Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/23/2018
12:45:59
Automatic Transfer Switch: Fault cleared on Source B.
03/23/2018
12:45:57
Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/23/2018
12:45:40
Automatic Transfer Switch: Fault exists on Source B.
03/23/2018
12:45:23
Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/23/2018
12:21:01
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018
12:20:29
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018
11:59:39
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018
11:59:05
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018
09:32:12
System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018
09:29:07
System: Configuration change. Event log web display time selection.
03/23/2018
09:28:45
System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018
08:35:07
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018
08:34:34
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018
21:59:50
Automatic Transfer Switch: ATS Communication established.
03/22/2018
21:59:30
Automatic Transfer Switch: 7-Segment display hardware initialized.
03/22/2018
21:59:30
Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
03/22/2018
21:59:19
System: Network service started. System IP is 198.18.130.40 from manually configured settings.
03/22/2018
21:59:19
System: Coldstart.
03/22/2018
20:58:05
Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018
20:58:03
Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/22/2018
20:57:46
Automatic Transfer Switch: Fault exists on Source B.
03/22/2018
20:57:39
Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/22/2018
20:57:28
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018
20:57:20
Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018
20:57:19
Automatic Transfer Switch: Fault cleared on Source A.
03/22/2018
20:57:18
Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/22/2018
20:57:03
Automatic Transfer Switch: Fault exists on Source B.
03/22/2018
20:57:01
Automatic Transfer Switch: Fault exists on Source A.
03/22/2018
20:56:44
Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/22/2018
20:56:44
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018
20:56:23
Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/22/2018
20:56:16
Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018
20:56:00
Automatic Transfer Switch: Fault exists on Source B.
03/22/2018
20:55:53
Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/22/2018
20:51:39
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018
20:51:12
Automatic Transfer Switch: Over frequency violation cleared on Source B.
03/22/2018
20:51:12
Automatic Transfer Switch: Over frequency violation cleared on Source A.
03/22/2018
20:51:07
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018
20:51:01
Automatic Transfer Switch: Over frequency violation on Source B.
03/22/2018
20:51:01
Automatic Transfer Switch: Over frequency violation on Source A.
03/22/2018
20:49:00
Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018
20:48:56
Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/22/2018
20:48:40
Automatic Transfer Switch: Fault exists on Source B.
03/22/2018
20:48:33
Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/22/2018
20:47:27
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018
20:46:59
Automatic Transfer Switch: Fault cleared on Source A.
03/22/2018
20:46:58
Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/22/2018
20:46:33
Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/22/2018
20:46:26
Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018
20:46:22
Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/22/2018
20:46:22
Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018
20:46:10
Automatic Transfer Switch: Fault exists on Source B.
03/22/2018
20:45:57
Automatic Transfer Switch: Fault exists on Source A.
03/22/2018
20:45:51
Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018
20:45:41
Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/22/2018
20:45:41
Automatic Transfer Switch: ATS has switched source. Source B is current source.