Over frequency violation on 7723

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Over frequency violation on 7723
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-06-25 11:05 PM . Last Modified: ‎2024-03-19 03:23 AM

0 Likes
0
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:05 PM . Last Modified: ‎2024-03-19 03:23 AM

Over frequency violation on 7723

hi all, we are having an issue with the ats, when it goes to generator power, it shows an abnormal log includes "over frequency violation" please find the annexed log.

Date Time Event
03/23/2018 19:51:18 System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018 19:47:52 Automatic Transfer Switch: Event counts cleared.
03/23/2018 19:44:49 System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018 19:44:32 System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018 19:37:01 System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018 19:33:09 System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018 19:30:04 System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018 14:33:51 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018 14:33:18 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018 13:53:24 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018 13:53:15 Automatic Transfer Switch: Fault cleared on Source A.
03/23/2018 13:53:14 Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/23/2018 13:52:58 Automatic Transfer Switch: Fault exists on Source A.
03/23/2018 13:52:42 Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/23/2018 13:52:42 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018 13:39:42 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018 13:39:12 Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/23/2018 13:38:28 Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/23/2018 13:38:28 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018 13:37:33 Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/23/2018 13:36:41 Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/23/2018 12:45:59 Automatic Transfer Switch: Fault cleared on Source B.
03/23/2018 12:45:57 Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/23/2018 12:45:40 Automatic Transfer Switch: Fault exists on Source B.
03/23/2018 12:45:23 Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/23/2018 12:21:01 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018 12:20:29 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018 11:59:39 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018 11:59:05 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/23/2018 09:32:12 System: Web user 'apc' logged out from 203.143.14.232.
03/23/2018 09:29:07 System: Configuration change. Event log web display time selection.
03/23/2018 09:28:45 System: Web user 'apc' logged in from 203.143.14.232.
03/23/2018 08:35:07 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/23/2018 08:34:34 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018 21:59:50 Automatic Transfer Switch: ATS Communication established.
03/22/2018 21:59:30 Automatic Transfer Switch: 7-Segment display hardware initialized.
03/22/2018 21:59:30 Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
03/22/2018 21:59:19 System: Network service started. System IP is 198.18.130.40 from manually configured settings.
03/22/2018 21:59:19 System: Coldstart.
03/22/2018 20:58:05 Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018 20:58:03 Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/22/2018 20:57:46 Automatic Transfer Switch: Fault exists on Source B.
03/22/2018 20:57:39 Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/22/2018 20:57:28 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018 20:57:20 Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018 20:57:19 Automatic Transfer Switch: Fault cleared on Source A.
03/22/2018 20:57:18 Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/22/2018 20:57:03 Automatic Transfer Switch: Fault exists on Source B.
03/22/2018 20:57:01 Automatic Transfer Switch: Fault exists on Source A.
03/22/2018 20:56:44 Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/22/2018 20:56:44 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018 20:56:23 Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/22/2018 20:56:16 Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018 20:56:00 Automatic Transfer Switch: Fault exists on Source B.
03/22/2018 20:55:53 Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/22/2018 20:51:39 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018 20:51:12 Automatic Transfer Switch: Over frequency violation cleared on Source B.
03/22/2018 20:51:12 Automatic Transfer Switch: Over frequency violation cleared on Source A.
03/22/2018 20:51:07 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018 20:51:01 Automatic Transfer Switch: Over frequency violation on Source B.
03/22/2018 20:51:01 Automatic Transfer Switch: Over frequency violation on Source A.
03/22/2018 20:49:00 Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018 20:48:56 Automatic Transfer Switch: Redundancy has been restored. Source B is available.
03/22/2018 20:48:40 Automatic Transfer Switch: Fault exists on Source B.
03/22/2018 20:48:33 Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
03/22/2018 20:47:27 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018 20:46:59 Automatic Transfer Switch: Fault cleared on Source A.
03/22/2018 20:46:58 Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/22/2018 20:46:33 Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/22/2018 20:46:26 Automatic Transfer Switch: Fault cleared on Source B.
03/22/2018 20:46:22 Automatic Transfer Switch: Redundancy has been restored. Source A is available.
03/22/2018 20:46:22 Automatic Transfer Switch: ATS has switched source. Source B is current source.
03/22/2018 20:46:10 Automatic Transfer Switch: Fault exists on Source B.
03/22/2018 20:45:57 Automatic Transfer Switch: Fault exists on Source A.
03/22/2018 20:45:51 Automatic Transfer Switch: ATS has switched source. Source A is current source.
03/22/2018 20:45:41 Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.
03/22/2018 20:45:41 Automatic Transfer Switch: ATS has switched source. Source B is current source.

 

Labels
  • Labels:
  • Getting Started
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore