Ouch. Wrong plug on several units.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Ouch. Wrong plug on several units.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

0 Likes
5
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

Ouch. Wrong plug on several units.

We goofed.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUM3000RMXL2U

Unfortunately, we didn't want the NEMA L5-30P for supply power. And we knew better. πŸ˜•

There seem to be no available options for changing the input configuration, even though the back of the unit seems removable (see attachment).

Are there any "unenumerated" options that can be obtained -- the entire supply module for this thing?

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:07 AM . Last Modified: β€Ž2024-02-14 10:33 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:07 AM . Last Modified: β€Ž2024-02-14 10:33 PM

120v x 80% x 30A = 2880. Note, VA != V x A, though it's a good enough approximation for many uses.

We've recycled 3000VA's into lower-power applications with no problems in the past. The "proper" way is to use an L5-30P To L5-20R converter cable with a 20A circuit breaker. I'm not sure APC makes such a product, but Google suggests a competitor does. I'm told that the purpose of the circuit breaker is to guarantee that you're not overloading the 20A connectors, since it is possible to have multiple L5-20 outlets on a larger circuit of some sort, and you could build a situation where the SU3000 is trying to draw more than 16A, and the panel breaker wouldn't break the circuit. Were you to be certain that the circuit was only a 20A circuit, you could possibly use a cable like Stayonline's #6297, but you might want to check with your AHJ first as to whether or not it will pass inspection.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

Yikes. Looks as if the 3000 won't accommodate a 20A plug at all. Is that right?

We'll have to have our electrical guys do the work. πŸ˜•

I love grant processes so much! πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

We've had customers who've used a 3k on a 20A outlet without problems, so I assume it wouldn't really matter. I don't understand why the document doesn't explain that in clearer detail.

Anyways, I mean if you're not paying for it, why not make it happen...right?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:06 AM . Last Modified: β€Ž2024-02-14 10:33 PM

You're limited to 1800VA if you use a 20A plug. 120v x 80% x 20 = 1800. The reason for 80% is NEC only allows 80% of the rated current for continuous use.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-28 03:07 AM . Last Modified: β€Ž2024-02-14 10:33 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:07 AM . Last Modified: β€Ž2024-02-14 10:33 PM

I would take a look at this K-Base first.

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184


Then let me know if you have questions beyond that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 03:07 AM . Last Modified: β€Ž2024-02-14 10:33 PM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 03:07 AM . Last Modified: β€Ž2024-02-14 10:33 PM

120v x 80% x 30A = 2880. Note, VA != V x A, though it's a good enough approximation for many uses.

We've recycled 3000VA's into lower-power applications with no problems in the past. The "proper" way is to use an L5-30P To L5-20R converter cable with a 20A circuit breaker. I'm not sure APC makes such a product, but Google suggests a competitor does. I'm told that the purpose of the circuit breaker is to guarantee that you're not overloading the 20A connectors, since it is possible to have multiple L5-20 outlets on a larger circuit of some sort, and you could build a situation where the SU3000 is trying to draw more than 16A, and the panel breaker wouldn't break the circuit. Were you to be certain that the circuit was only a 20A circuit, you could possibly use a cable like Stayonline's #6297, but you might want to check with your AHJ first as to whether or not it will pass inspection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of