Older firmware to suit AP9631

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Older firmware to suit AP9631
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
avecchio
Crewman avecchio
Crewman

Posted: ‎2024-01-28 08:43 PM

0 Likes
3
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-28 08:43 PM

Older firmware to suit AP9631

I have 2 LX Single phase Symmetra UPSs amongst other Symmetra UPSs.

Site A is AP9631 NMCv2 05 sy v5.1.7 aos v5.1.7 bootmon v1.0.2
Site B is AP9631 NMCv2 08 sy v6.8.0 aos v6.8.2 bootmon v1.0.9


I have found that I can download v7.1.2 for the symmetra
https://www.se.com/au/en/download/document/APC_SY_712_EN/
but ideally would like to take the v5.1.7 to v6.8.0 prior to a possible v7.1.2 update.
that way both units are on same firmware...


The newer GUI in v6 compared to v5 has more options, but worried about 5.1.7 - > 7.1.2

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Janeway Teken
Janeway

Posted: ‎2024-01-29 06:04 AM

1 Like
0
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 06:04 AM

Reach out to APC Support to obtain the 6.X.X firmware. From past experience you have a 50-50 chance of seeing success vs failure. 🤦‍♂️

 

So, you asking to stage the upgrade path is not only prudent but shows experience & competence. 👍 Not sure if your team has any (NMC) units set aside as test spares but would kindly suggest you read over the APC FAQ about how to recover the NMC / restore the unit to factory default state on one if you do. ☝️

 

Having the ability to flash, test, and practice on the bench as they say. Offers critical insight and prepares you for most outcomes should they arise. Insure you have the serial cable for the NMC on hand in case things go sideways! 🙁

 

Let us know how it turns out - Good luck 🤞 

Reply

Link copied. Please paste this link to share this article on your social media post.

avecchio
Crewman avecchio
Crewman

Posted: ‎2024-01-30 02:13 PM

0 Likes
0
857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-30 02:13 PM

I've got a spare AP9619 that we replaced with a AP9641 in Site C recently but the AP9619 is a v1 NMC if things go pair shape.
Site B is now running on 7.1.2 - updated skipping download logs to accept update
   Only issue was the UPS name had invalid characters in the string after update.

Site D has a AP9619 but have ordered a AP9641 for it as well for planned maintenance.

Site A is the hold out waiting for a response from anztech.

 

We monitor the 4 sites with SNMP via PRTG which works well.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

avecchio
Crewman avecchio
Crewman

Posted: ‎2024-01-30 06:35 PM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-30 06:35 PM

After contact from SE Support, was advised I could got from v5.1.7 to v7.1.2

Due to the AP9631 only having telnet enabled, and without having to setup ssh, using the firmware tool FTP option updated the firmware.

Success !!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of