Old AP7750 with AP9617 no light on NMC

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Old AP7750 with AP9617 no light on NMC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Joe88
Crewman Joe88
Crewman

Posted: ‎2024-10-25 05:35 AM

0 Likes
3
738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 05:35 AM

Old AP7750 with AP9617 no light on NMC

We have an old AP7750 that seems to work as far as powering our equipment and switching inputs as needed, but the NMC doesn't power on.

 

There are no lights on the AP9617 when inserted into the AP7750, the reset button does nothing and I've visually inspected the slot and don't see anything wrong with it.

 

We've tried to reseat the card, tested in a SmartUPS to verify it powers on and can connect over the network and the card appears to be working.

 

We are also able to connect to the AP7750 using a serial cable but doesn't seem like there are any configurable settings.

 

Any suggestions why and if there is a way to fix the old AP7750?

 

Thanks for the help!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-25 07:11 AM

0 Likes
2
731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 07:11 AM

What exactly is the history of this AP9617 NMC?!? Meaning it was (always) confirmed to be installed into the ATS?!?

 

If not and it was installed into a UPS the NMC would need to be flashed with the correct ATS firmware.

 

Since you can SSH into the ATS what does the system indicate as to the loaded firmware upload a screen shot for review.

 

Regardless, if we assume it’s the factory NMC that came with the ATS. Format the NMC by pressing and holding down the reset button for more than 20 seconds then release.

 

It will take about 30-60 seconds to format and come back up. Once complete the NMC will be in a default state and DHCP will be active and the user name / password is all lower case: apc

 

NOTE: This NMC is very old and slow and outdated. As such you can only access the website via HTTP (Not) HTTPS. The pages are extremely slow to load and you must use IE in legacy / compatibility mode.

 

Lastly, you must always logout . . . 

Otherwise you’ll see a message saying another person is logged in already etc. You can resolve this by entering into the URL at the end to logout.htm or whatever the system indicates. 

Let me know . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Joe88
Crewman Joe88
Crewman

Posted: ‎2024-10-25 02:17 PM

In response to Teken
0 Likes
1
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 02:17 PM

Thanks for the reply, the card doesn't power on in the AP7750, no lights, no status, the reset does nothing, there's no link on the connected switch, etc..  Tried a different AP9617 and same deal, both cards work in an old SmartUPS, they power on and get an IP address.

 

When its connected in the SmartUPS the lights come on, we get a link and I can reset and logon to the card over the network. It has the APC firmware for the AP vs UPS so believe it to be the correct card but I can't be 100% sure.

 

Here is screenshot of the terminal with firmware version on the AP7750.  Is there an admin password over serial connection that gives us access to some basic config?

Joe88_0-1729890781062.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-29 04:50 AM

In response to Joe88
0 Likes
0
636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-29 04:50 AM

The user name in a default state is all lower case: apc

 

I have appended the full user manual for this legacy device here:

 

https://download.schneider-electric.com/doc/SPD_ASTE-6Z6K9J_EN/ASTE-6Z6K9J_R3_EN.pdf

 

Pay special attention as it relates to DHCP, Telnet, SSH, Web Setup.

 

Given you have proven the card turns on in a UPS. I would open up the ATS to see if there is any thing blocking the NMC from making contact from dust, corrosion, bugs etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore