Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Oids for the PDU Models AP8841 and AP8865
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2910:11 PM. Last Modified: 2024-03-1201:14 AM
Oids for the PDU Models AP8841 and AP8865
Could you please help me in getting the updated undp file for APC PDU AP88** models for solarwinds and I also need OIDs for the same model to pull some general data such as model, uptime, load, power usage on the banks etc. Google was not that helpful in finding the updated undp file and OIDs for the PDU. Any help will be appreciated.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2910:11 PM. Last Modified: 2024-03-1201:14 AM
Hi Rajesh,
I don't know what a undp file is but APC does not provide them. It might be something provided by or used by SolarWinds.
What we do provide is the APC PowerNet MIB which contains the OIDs for all of the APC devices (excluding NetBotz which contain their own MIB).
The MIB is available at http://www.apc.com/tools/download/index.cfm and select Filter by Software/Firmware and look for Firmware Upgrades - MIB. From there, you can download the PowerNet MIB to compile/load into SolarWinds.
For AP8XXX series Rack PDUs, all of the PDU specific OIDs are located under .iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2 / .1.3.6.1.4.1.318.1.1.26 . There are several subtrees under there depending on the type of device.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2910:11 PM. Last Modified: 2024-03-1201:14 AM
Hi Rajesh,
I don't know what a undp file is but APC does not provide them. It might be something provided by or used by SolarWinds.
What we do provide is the APC PowerNet MIB which contains the OIDs for all of the APC devices (excluding NetBotz which contain their own MIB).
The MIB is available at http://www.apc.com/tools/download/index.cfm and select Filter by Software/Firmware and look for Firmware Upgrades - MIB. From there, you can download the PowerNet MIB to compile/load into SolarWinds.
For AP8XXX series Rack PDUs, all of the PDU specific OIDs are located under .iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2 / .1.3.6.1.4.1.318.1.1.26 . There are several subtrees under there depending on the type of device.
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.