OID for product family

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
153

OID for product family

This question was originally posted by Stuart on APC forums on 6/5/2016


What OID are other folks using, to identify the 'family' of APC product family?

I start with upsBasicIdentModel.0, which gets me responses like "Smart-UPS 5000", Symmetra, Silcon, etc.  Pretty useful.

But with all other APC products, I fall back to "experimental.2.2.1.5.1", which gets me values like "Rack PDU" and "Modular PDU".  Also pretty useful ... but I dislike relying on 'experimental' OIDs.

I suppose I could parse sysDescr, extract "AN1", and build a table mapping things like 'rpdu2' to "Rack PDU" and 'xrdp' to "Modular PDU".  Seems crude to me, but hey.

Does anyone have a spiffier way of determining, via SNMP, what 'product family' hosts the mgmt card you are currently querying?

--sk

Tags (2)

Accepted Solutions
bbiandov_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
153

Re: OID for product family

This was originally posted on APC forums on 6/14/2016


you can parse SNMPv2-MIB::sysDescr.0 (OID .1.3.6.1.2.1.1.1.0) for MN:xxxxx and that's the model # Here's what the string looks like in one of mine:

SNMPv2-MIB::sysDescr.0 = STRING: APC Web/SNMP Management Card (MB:v3.9.2 PF:v3.9.0 PN:apc_hw02_aos_390.bin AF1:v3.7.4 AN1:apc_hw02_rpdu_374.bin MN:AP7832 HR

:B2 SN: ZA0746009879 MD:11/14/2007)

You get more than just a model number 🙂

~B

See Answer In Context

1 Reply 1
bbiandov_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
154

Re: OID for product family

This was originally posted on APC forums on 6/14/2016


you can parse SNMPv2-MIB::sysDescr.0 (OID .1.3.6.1.2.1.1.1.0) for MN:xxxxx and that's the model # Here's what the string looks like in one of mine:

SNMPv2-MIB::sysDescr.0 = STRING: APC Web/SNMP Management Card (MB:v3.9.2 PF:v3.9.0 PN:apc_hw02_aos_390.bin AF1:v3.7.4 AN1:apc_hw02_rpdu_374.bin MN:AP7832 HR

:B2 SN: ZA0746009879 MD:11/14/2007)

You get more than just a model number 🙂

~B