Network monitoring problems with all 3 UPS units from management servers

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network monitoring problems with all 3 UPS units from management servers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

0 Likes
3
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

Network monitoring problems with all 3 UPS units from management servers

Hi All,

I seem to be having problems monitoring my 3 APC Smart UPS 6000XL units using any kind of management software.  I have set the software up on two different servers now and have ping monitors on over 100 devices that all respond normally.  However when I add the UPS units they keep coming back as not responding and when I run pings to the units from a command prompt I get no reply.  Is there a known bug with the management cards on these units?  As it stands it is impossible to add them to the monitoring systems as it says they are down every few minutes!  It seems that others have experienced this but found no solution. Does anyone know how to sort this? Are there settings I need to change on the UPS?

http://community.spiceworks.com/topic/255188-monitoring-server-can-t-ping-apc-ups-device

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

0 Likes
0
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

Thanks! And the "management software" - are we talking SNMP? If so, v1 or v3? v1 is only on by default. But that does not explain why the ping is not working properly.

Also, If you can web and Telnet, that's fine. SSH replaces telnet so if telnet worked, SSH is disabled.

I'd want to compare the IP/subnet mask/gateway for typos in those settings or anything else that could potentially cause a problem. But, if web and telnet work, then I think it is not likely but perhaps are these devices on their own VLAN or subnet? Just trying to narrow things down that are similar among these devices and then the devices you have that are working.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

0 Likes
0
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

Can you tell me what model of UPS Network Management Card is installed in these three UPSs? It is likely AP9631 or AP9619.

I'd also like to see the log files (event.txt, data.txt, config.ini) from at least 1-2 of them to review and that will likely help. (Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Are you able to successfully able to Web, Telnet, SSH, etc to these Network Management Cards? Are there other APC devices that respond successfully or are the other 100 devices other vendor's devices?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

0 Likes
0
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

Hi Angela,

Thank you for responding - sorry my reply is late I thought I would get an email alert when someone responded.  My Network Management cards are indeed AP9619.  I am able to Web and Telnet (haven't tested SSH yet) - the over devices I have are all from other vendors.  I'll get you those logs.

Regards

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:32 AM . Last Modified: ‎2024-03-05 12:37 AM

Thanks! And the "management software" - are we talking SNMP? If so, v1 or v3? v1 is only on by default. But that does not explain why the ping is not working properly.

Also, If you can web and Telnet, that's fine. SSH replaces telnet so if telnet worked, SSH is disabled.

I'd want to compare the IP/subnet mask/gateway for typos in those settings or anything else that could potentially cause a problem. But, if web and telnet work, then I think it is not likely but perhaps are these devices on their own VLAN or subnet? Just trying to narrow things down that are similar among these devices and then the devices you have that are working.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore