Network Mgmt card (AP9617) Warmstart, service start, restored comm, repeat

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network Mgmt card (AP9617) Warmstart, service start, restored comm, repeat
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
9
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

Network Mgmt card (AP9617) Warmstart, service start, restored comm, repeat

I have a RM1500 with a AP9617 network management card.  Seems like every weekend the card starts having "fits".  The fits seem to stop, but may repeat.  As an example this past weekend it start to fit Saturday morning 10:27 through 15:19 and then did it again on Sunday starting at 9:29 through 13:42.  During these times there were multiple repeats of these episodes.  The hardware firmware version is A~0 and the application module is the latest 3.7.2.  Here is a group of the error messages.

07/13/2013 10:27:27 UPS: Restored the local network management interface-to-UPS communication.
07/13/2013 10:27:00 System: Network service started. System IP is 192.168.x.y from manually configured settings.
07/13/2013 10:27:00 System: Warmstart.

Any thoughts?  I am about ready to yank the card since it doesn't seem to be doing me much good with these type of spewing messages and try to move to the serial cable.  No devices that are connected to the UPS have any type of power issues.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

It might be because the DHCP Option 43 is enabled by default for this card/firmware. Do you have access to set this on your DHCP server cause its probably rejecting an address if it is not set. Alternatively, you can disable this option via a serial connection and then let it get a DHCP address. I am just guessing this is the issue you may be having though for DHCP.

Vendor Specific Information - (option 43) - this option encapsulates the APC cookie and the Boot Mode Transition setting.

The NMC uses this option in a DHCP response to determine whether the DHCP response is valid. This option contains an option in a TAG/LEN/DATA format, called the APC Cookie. This is disabled by default on NMC2 devices.


APC Cookie. Tag 1, Len 4, Data “1APC”


Option 43 communicates to the NMC that a DHCP server is configured to service devices. Following, in hexadecimal format, is an example of a Vendor Specific Information option that contains the APC cookie:

Option 43 = 0x01 0x04 0x31 0x41 0x50 0x43

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

"Official" procedure is to braindead the UPS and essentially turn it off and force it to discharge its capacitors but I never do that unless there is something wrong with the UPS to begin with. My personal recommendation for your situation is to just go ahead and remove it hot and there will be no effect to the UPS load or the UPS itself. You can also just install a new one hot too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

I have a RM1500 with a AP9617 network management card.  Seems like every weekend the card starts having "fits".  The fits seem to stop, but may repeat.  As an example this past weekend it start to fit Saturday morning 10:27 through 15:19 and then did it again on Sunday starting at 9:29 through 13:42.  During these times there were multiple repeats of these episodes.  The hardware firmware version is A~0 and the application module is the latest 3.7.2.  Here is a group of the error messages.

07/13/2013 10:27:27 UPS: Restored the local network management interface-to-UPS communication.
07/13/2013 10:27:00 System: Network service started. System IP is 192.168.x.y from manually configured settings.
07/13/2013 10:27:00 System: Warmstart.

Any thoughts?  I am about ready to yank the card since it doesn't seem to be doing me much good with these type of spewing messages and try to move to the serial cable.  No devices that are connected to the UPS have any type of power issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

Could you post the full event.txt for me to review please? (Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA... and again, I just need event.txt) You can post it as an attachment on your reply - just make sure you use the advanced editor option.

Also, I'd start by reviewing this to better understand what the message mean since it does not typically deal with any "power issues."

Why does my Network Management Card report warmstarts and coldstarts? | FAQs | Schneider Electric US

Once I review the event.txt, I can better suggest how to move forward. This could be related to times of the day where you have heavy network traffic (does that sound likely) and the management card is having trouble contacting its gateway as described in the article above?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

I have enclosed both the event and data files (just in case.)

I have reviewed the link previously and didn't see anything applicable.

Time of day nor network traffic is likely.  The weekend is the "slow" time for traffic

Attachments
data.txt.zip
event.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

Ok I am looking at it now. I do see a few of these in there:

  • System: TCP/IP stack failure. Module: tfSheapFree-assertion error line 610, file(.\treck\source\trsheap.c)

  • System: TCP/IP stack failure. Module: tfUnLock-Lock is Corrupt

Let me see what I can find out more about those tomorrow. I haven't seen the second one before.

If I wasn't able to inquire further on what those specifically refer to and had to answer now, the first thing I'd do is reset the card to defaults (including or excluding TCP/IP settings depending on if you can configure those again) and reconfigure and monitor.

I'll post back tomorrow once I see what those mean if you just want to hang back.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

Any updates and/or insights based on the files?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

Sorry for the delay drumidwest. Just re-checked on my request. embarassed

Basically - not good. Something is corrupted badly and obviously it shouldn't be. We should reset the entire card to defaults (you can back up your config.ini file to save your configuration) and monitor and if it happens again, the flash memory on the card could be faulty also and may need to be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

Thank you. I will reset it, though I believe I had to do that once before since it would not play nice with our DHCP server. If that doesn’t solve it I will presume the card is bad and move on from there.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

0 Likes
0
2067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:01 AM . Last Modified: ‎2024-03-05 10:30 PM

It might be because the DHCP Option 43 is enabled by default for this card/firmware. Do you have access to set this on your DHCP server cause its probably rejecting an address if it is not set. Alternatively, you can disable this option via a serial connection and then let it get a DHCP address. I am just guessing this is the issue you may be having though for DHCP.

Vendor Specific Information - (option 43) - this option encapsulates the APC cookie and the Boot Mode Transition setting.

The NMC uses this option in a DHCP response to determine whether the DHCP response is valid. This option contains an option in a TAG/LEN/DATA format, called the APC Cookie. This is disabled by default on NMC2 devices.


APC Cookie. Tag 1, Len 4, Data “1APC”


Option 43 communicates to the NMC that a DHCP server is configured to service devices. Following, in hexadecimal format, is an example of a Vendor Specific Information option that contains the APC cookie:

Option 43 = 0x01 0x04 0x31 0x41 0x50 0x43

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore