Opinons/experiences with natural gas vs diesel fuel backup genset for Data Centre. Which one is better?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:34 AM
Opinons/experiences with natural gas vs diesel fuel backup genset for Data Centre. Which one is better?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:35 AM
I've done both. Both have advantages and disadvantages. Diesel requires fuel storage tanks, fuel maintenance, and is transported in by truck. That can be a problem in an ice storm that lasts 6 days, taking power lines down and stopping traffic. However, with gaseous gen sets, the pressure from the source is critical for proper operation, you share that pressure/flow with everyone else on the block and building, and gas is the first thing they cut off when there's a fire, flood, earthquake, etc in the area. Be careful when your engineering firm puts the gas lines downstream of the building boilers to save pipe costs.
The decision of gaseous vs diesel really depends on your application, installation location, local code authorities, budget constraints, and runtime requirement. For the most part, the diesel limitations and compromises can be overcome with additional engineering, installation, and processes/contracts.
If I had to answer in one word: Diesel
Cummins has some good reading on this subject.
Chapter 2 has a good review of things to consider for fuel supply considerations diesel vs gas
Application manual Cummins Liquid cooled generator sets, PRELIMINARY DESIGN: Chapter 2
http://www.cumminspower.com/www/literature/applicationmanuals/t-030_p10-22.pdf
Application manual Cummins Liquid cooled generator sets, FUEL SUPPLY: Chapter 6
http://www.cumminspower.com/www/literature/applicationmanuals/t-030_p115-132.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:35 AM
you may want to look into purchasing a fuel polishing system. Check out ESI fuel management:
http://www.fuelmanagement.com/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:34 AM
I read the topic of this thread and thought that I'd be able to pop in and discuss the merits of diesel versus natural gas and I find that TechTuff shares my thoughts exactly.
In my opinion, natural gas is not an "uninterruptible supply" of fuel. Many times, a power outage is caused in an area because of local construction cutting through/near power lines. Guess what commonly shares right-of-way underground w/ the power....
Of course, you could build an onsite storage tank for the gas, but most companies are not comfortable storing a "bomb" on their campus.
I'd look at diesel and a good contract with a couple of fuel suppliers to keep the tanks full.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:34 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:34 AM
I've had both power data centers.
Being in Canada, where it tends to get a tad chilly in the winter, Natural Gas is a high priority service. Gas service is restored faster than electricity here.
We use a large Natural Gas generator. We don't have issues with storing large quantities of deisel, don't have to worry on getting trucks to deliver the stuff. The generator runs cleaner with Natural gas.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:34 AM
I think that Natural Gas Gensets are Green products.
Also, I would consider liquefied natural gas sources to provide energy to DataCenter. At list the power backup is a kind of mixture of Gas & Diesel to get Green Data Center.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:25 PM . Last Modified: 2024-03-19 03:34 AM
Opinons/experiences with natural gas vs diesel fuel backup genset for Data Centre. Which one is better?
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.