2 x Smart-UPS SRT 2200 with NMC3 and temperature probe set up as redundant UPSs.
"High" temp is set to 24 degrees C, "Maximum" to 27 degrees C.
NMC Logs show server room got to 24 degrees at 8:24 AM when the door was left open. Temperature never reached 27 degrees; after 8 minutes it dropped back below the 24 degree threshold.
Control Policy on both NMCs is "Environment: A critical fault exists for integrated Environmental Monitor input contact ({name} at {location}): Graceful shutdown."
Here's what's in the PCNS log from the server that was shut down:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-06 11:13 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-06 11:57 AM . Last Modified: 2023-06-06 12:06 PM
Bill, you're correct that the one server that shut down has "Temperature Probe 1 Out Of Range" enabled for shutdown in PCNS and the others do not. So I need to fix that.
But, back in NMC, when I add a Control Policy, I'm offered the choice of "Warning" or "Critical".
I chose "Critical."
I had expected the NMC would only signal shutdown if the "Critical" threshold was passed. Not the "Warning" threshold. That's not correct? If so, what's the point of having Policies configurable for the two thresholds?
The goal was to have the warning at 75 F so one of the people who receives the notifications can block the door open and set up a box fan, where shutdown can be averted by keeping the temp below 80 F until air-conditioning is restored.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-07 11:57 AM
PowerChute does not differentiate. It will react to either as a critical event. The solution is to add a second AP9335 to port two. Configure port two with the high temp threshold that will send a notification.
PowerChtue will only react to port one so configure port one with the max temp threshold that will command PowerChute off.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-07 12:44 PM
@BillP , thanks for your reply!
If I leave the NMC configured as it is--to send a shutdown signal at 27 C--and disable Shutdown on the temperature violation Event in PCNS, will the NMC shut the servers down at 27 C? In other words, is the root of my issue that--at least on this one server--over-temperature shutdown is configured in both NMC and PCNS, when, given my objectives (notification at 24 C, shutdown at 27 C), it should only be configured on the NMCs?
Or does PCNS ignore the shutdown signal if it hasn't also been enabled in the PCNS Event?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-08 12:22 PM
Are you using an AP9335 with the AP9810? If so you will need to create two Control Policies. One for the AP9810 and one for AP9335T/TH
On the AP9810 jumper
Zone A Com to Output Com
Zone A NC to Output NC
When the Max temp threshold is breached, the IO state changes, and the UPS powers off and signals PowerChute. PowerChute will shutdown because of the critical UPS turn off event.
PowerChute should not be configured to shutdown for a temperature threshold violation and should not be configured to power off the UPS or Outlet Group.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-09 06:38 AM
I won't be at this client again until Monday, so SKUs are hard to come by at the moment. But we are NOT using AP9810s. The thermal sensors connect directly to the NMC3s.