NMC restarts after login

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC restarts after login
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
BBoozer
BBoozer
Cadet

Posted: ‎2025-01-15 07:37 AM

0 Likes
3
467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-15 07:37 AM

NMC restarts after login

I have been hitting a wall finding issue like this. I have 2 of 3 devices in a remote office that shows the NMC restart after supplying login credentials, so I can never get in. One of them is sending SMTP messages out showing it restarts. On my end, all I see is a hang and eventual web page timeout. Monitoring pings shows it drop and restart. 

 

Ironically, the only reason I was logging in is to change the SMTP server address.

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2025-01-16 04:31 AM

0 Likes
2
441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-16 04:31 AM

Please call out the model and what NMC firmware is currently installed. Both information can be obtained via the LCD Menu if present.

 

The model number can be seen physically on the face of the NMC card. The NMC has a watch dog timer and will reset the network link if it detects a problem.

 

I would highly suggest you move the Ethernet cable to another port and see the results. If there are three NMC in the same building having issues I would be looking at that switch really hard.

 

Especially the verbose logs on the switch to determine when this started and the frequency.

 

Questions Ask . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

BBoozer
BBoozer
Cadet

Posted: ‎2025-01-17 11:33 AM

In response to Teken
0 Likes
1
404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-17 11:33 AM

Would LOVE to! However, as stated, REMOTE location. No IT on site. No one there I trust to understand what a UPS & PDU are, regardless of the big APC on it. 

 

Also, for those reading comments: DO NOT try to post on r/APC on Reddit. It is not for Schneider, but Animals in People Clothes (apparently a thing). Lots of posts about UPSs. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-01-20 03:52 AM

In response to BBoozer
0 Likes
0
402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-20 03:52 AM

Obviously your choices are quite limited if you’re not going on site or can’t trust anyone to move a Ethernet cable to another switch port / eye ball a label! 🤦‍♂️

 

Any serious remote installation would have at least VPN or KVM.

 

The most basic review of the switches verbose error logs must be seen. It will literally tell you if the port is having issues from flapping, RX/TX, packet dropped, etc.

 

In 2025 reviewing the logs from a Syslog, NMS, and the appliance itself is a minimum to be in place.

 

What do they show?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore