NMC-controlled UPS shutdown in a mixed PCNS and non-PCNS environment

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC-controlled UPS shutdown in a mixed PCNS and non-PCNS environment
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 06:25 AM . Last Modified: ‎2024-03-04 11:36 PM

0 Likes
1
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:25 AM . Last Modified: ‎2024-03-04 11:36 PM

NMC-controlled UPS shutdown in a mixed PCNS and non-PCNS environment

Hi there,

Been reading this great forum for over a week already. I've studied almost all the topics regarding NMC and PCNS, also read the article written by Steve Jenkins, viewed the shutdown charts and other documents, but it looks as my case is a bit special after all, so I decided to ask for some help.

To begin, I'll describe my use case first. I have the SUA750I with AP9617 NMC installed and properly configured and functioning. The connected equipment is quite diverse; there are two workstations (Windows and Linux), a Synology NAS, and a SOHO wifi router running some custom wrt rom. These devices aren't operating constantly, and are turned on and off independently on demand, but they are all powered from this very UPS in question!

The main reason for adding the NMC was to create a single command point, which would signal all the hosts in case of power failure, then wait for some time until the hosts shutdown, and finally put UPS to sleep state without waiting for the Low Battery Delay to elapse, as it would happen with the PCNS to initiate the UPS Turn Off process. The reason I want the UPS to early shutdown is to preserve battery life, since another power failure can potentially happen soon after the first one. Also, I just don't need the UPS to run that long.

Now, not all hosts are PCNS clients in my environment. For example, NAS supports only SNMP UPS (uses NUT), while the router and the linux (use APCUPSD) machine read UPS status via pcnet (PCNS protocol), which lacks full protocol functionality. Thus, all the hosts, except Windows machine, rely solely on OB and LB (on-battery, low battery) flags to trigger any action (be it shutdown, drive unmount etc), but they neither understand the PCNS graceful shutdown command, nor they can signal back the UPS to make it turn off. Ideally, I'd like to use the LB flag as the key indicator, that the time for shutdown has come! This way, I can configure LDB on NMC to decide when the shutdown process starts on the hosts, and I don't need to extra mess with configuring other triggering conditions (in respond to the OB flag), since PCNS, NUT and APCUPSD are hard-coded to shutdown the systems as soon as they receive the LB signal. I get perfect shutdown synchronization, even if any host was turned ON after the power has failed.

The question is how to signal UPS to perform an early shutdown, since PCNS are mostly not available to tell him to do so. If I set the LBD large enough, the hosts will shutdown quicker, but the UPS will continue wasting its energy counting down until the shutdown timer, which equals LBD, elapses. I am now contemplating on whether to buy the AP9630 NMC, which, as I learned from neighbor topics, is able to perform Controlled Early Shutdown with sending the graceful shutdown command to all the hosts. I'm not sure this is what I exactly need, because graceful shutdown will not be understood by the non-PCNS clients. Is there a way to configure the AP9630 to always set the LB flag whenever the CES meets any of the condition configured? Or, the only way to get the LB flag is when the LBD condition occurs? Then, maybe, using the CES condition of matching the remaining runtime (which should be set to a smaller value than the LBD), will shutdown the UPS after the LBD condition occurred, thus, the hosts must've been shut down already. Am I moving in the correct direction? Could you please share your thoughts and recommendations?

P.S. Is Controlled Early Shutdown on NMC2 supported on SUA750I?

Thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apcupsd
  • NMC
  • nut
  • pcns
  • shutdown
  • sua
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 06:25 AM . Last Modified: ‎2024-03-04 11:36 PM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:25 AM . Last Modified: ‎2024-03-04 11:36 PM

Controlled Early Shutdown, aka Load Shedding, should work on a SUA750I with an NMC2. Another option with the latest firmware on NMC1 if you're okay with shutting down after a certain amount of time on battery is to set the OnBatteryShutdownDelay in config.ini. I've attached such a config.ini file.

See Answer In Context

Attachments
config.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 06:25 AM . Last Modified: ‎2024-03-04 11:36 PM

0 Likes
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:25 AM . Last Modified: ‎2024-03-04 11:36 PM

Controlled Early Shutdown, aka Load Shedding, should work on a SUA750I with an NMC2. Another option with the latest firmware on NMC1 if you're okay with shutting down after a certain amount of time on battery is to set the OnBatteryShutdownDelay in config.ini. I've attached such a config.ini file.

Attachments
config.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of