Metered PDU Control Console - Up Time Field

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Metered PDU Control Console - Up Time Field
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

0 Likes
5
667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

Metered PDU Control Console - Up Time Field

I have an AP7894 Metered PDU that has been installed and powered since Nov2009. The UP Time field displayed on the main screen of the control console menu reports that the PDU has been up for only 60 days. I expect the counter is rolloing over at some point...can anyone explain this, is there any way for me to determine the actual Up Time for a PDU that has been running for several years?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

Ahh, OK. Let me enter a request to clarify that. And you're welcome! Hope you have a nice day too. smile

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

I just got this same question from Brian this morning as part of your account team from the email you sent smile so you'll probably get an answer there too.

The uptime you see for any management card enabled device is for the network management interface only. This applies to a UPS, Rack PDU, etc as none of the devices themselves store an uptime for the device as far as I know. So basically, you are only seeing the uptime of the management interface and for a Rack PDU, there is no way to tell how long the device's load, outlets, etc have been up.

P.S. I don't think the counter rolls over for at least like 300-400 days at most.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

Ok, thank you.

So the fact that the NMC indicates it's been up for more than 60, is it safe to assume that the source power for the AP7894 PDU has not been interuppted for that period of time?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

Correct. So basically, the management card can reboot without the PDU rebooting but not vice versa (since this a metered Rack PDU and does not offer outlet control - even so, controlling outlets yourself does not affect management card uptime).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

Vg, TY.

Jsut an FYI, the manual is a bit misleading.....

From Console Control section of the on line manual...

Up Time field reports how long the Rack PDU has been running since it was last turned on or reset

Thanks again, and good day


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

0 Likes
0
666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:59 AM . Last Modified: ‎2024-03-18 01:03 AM

Ahh, OK. Let me enter a request to clarify that. And you're welcome! Hope you have a nice day too. smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of