Hey so we recently got some replacement batteries for the SMT750i , only we found out that our SMT750i was missing the wiring connecting the batteries to the UPS.
Does anyone know if we can get those separately and where?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-19 03:17 AM . Last Modified: 2024-06-19 03:19 AM
Your options are to purchase another RBC that includes everything such as the batteries, interconnects, fuse, and Anderson connectors.
The second option is to simply make your own cables using 10 AWG stranded copper wire that is 600 VDC / 105’C rated. The original connectors are high quality Molex branded connectors that have a locking tab.
You can use any equivalent connector that is so rated for the ampacity. You’ll obviously need to purchase the correct Anderson Plug for the RBC.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-18 05:15 AM . Last Modified: 2024-06-18 05:25 AM
Are you missing all the interconnecting cables including the Anderson plug that goes into the UPS?!?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-19 12:44 AM
Yes, they were likely thrown away when the old batteries were removed
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-19 03:17 AM . Last Modified: 2024-06-19 03:19 AM
Your options are to purchase another RBC that includes everything such as the batteries, interconnects, fuse, and Anderson connectors.
The second option is to simply make your own cables using 10 AWG stranded copper wire that is 600 VDC / 105’C rated. The original connectors are high quality Molex branded connectors that have a locking tab.
You can use any equivalent connector that is so rated for the ampacity. You’ll obviously need to purchase the correct Anderson Plug for the RBC.