Looking at a SMT-1500, need to monitor a PC and NAS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Looking at a SMT-1500, need to monitor a PC and NAS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:58 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
15
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:58 AM . Last Modified: ‎2024-03-13 11:36 PM

Looking at a SMT-1500, need to monitor a PC and NAS

Like the title states, I need to monitor a pc and a NAS. I see there are two ports (USB port and UPS monitoring port). Can I use both ports individually (one for the pc, and one for the NAS) to monitor each and gracefully bring each down in the event of a power outtage?

If that is not possible, is there a recommended solution?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

Well....thats really really odd....Will there be another cable that will work with the RJ45 to USB or ist there one in planning? Cause I can't believe ist a brand new UPS an we write the year 2014 and it is not possible to conect more that one Server via USB which is delivered with a Software that supports up to 5 Agents...

Thanks for your Feedback and help anyways.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:58 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:58 AM . Last Modified: ‎2024-03-13 11:36 PM

via USB, yes. only one supported unit. you can use USB and serial at the same time on this unit though if you had a serial connection.

you are also only supposed to use USB/serial OR a network management card.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

rats.

I can't believe I'm saying this but it appears I'm in the market for a serial card to install on a win7 box. That's almost embarrassing to type.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

What you can do is to connect the PC into the UPS using either USB or Serial(UPS Monitoring Port) and installing PowerChute Business Edition. Using PCBE, you can run scripts that could possible turn off your NAS.

If your UPS comes with a network management card, it is equipped to send SNMP traps. The software that works with an NMC (network management card) is PowerChute Network Shutdown which can also run scripts.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

which model NAS do you have by the way? some models support USB and serial connectivity for shutdown, others use SNMP like JonPro mentioned.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

Netgear ReadyNAS Ultra 4. It supports USB connectivity for shutdown as does the PC. There is where the problem lies. Need the PC to gracefully shut down as well as the NAS, and it sounds like only one can be brought down without an add in card to the UPS.

Message was edited by: stumpy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

Interesting.

I can't seem to find a good picture of the serial cable, but from the information I'm able to drum up it appears to be an RJ-45 to Serial cable. Is there another RJ-45 cable terminated with something other than serial that would support the same transmission of data? For example, my current APC has an RJ-45 to USB cable. Could that be used to replace the serial cable?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

negative. the ports have different pinouts. the RJ-45 to serial cable you refer to is correct - part # 940-0625A for the 6 foot or 940-1525A for the 15 foot version.

the other cable is AP9827 and only works with some Back UPS and older Smart UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:36 PM

LOL i understand that. you will want to use the powerchute business edition software if you do pursue this to get a graceful shutdown. you just need to install the single node agent to talk to the UPS via serial.

if you have enough runtime and don't care about a graceful shutdown on your computer, then you can skip this cable and do most of your voltage monitoring, etc via the front LCD.

what exactly do you want to monitor? voltage, alerts, etc?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

I'm back Angela (spoke to you over 3 years ago about this product)!  Still using the SMT-1500 and its been fantastic.  However, I'm moving to a new computer that does not have a serial connection nor does it have room for a serial card.  Can I use the AP9827 (RJ45-USB) cable to connect the pc to the UPS?

I currently have the native USB port connected to my Windows Server 2012 server and it recognizes how full the battery is.  Can I use that second cable (the AP9827) to connect the RJ45 port to my Windows 8 desktop to identify the status of the battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

Hi,

The AP9827 will not work with the SMT. Your options are

1 - purchase a USB to serial converter (I use a Hawking but there are many others that work)

2 - purchase a network management card and switch from USB native to PowerChute Network Shutdown

3 - script the Windows Server to send shutdown signal to the Windows 8 system

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

Hi there, I have the very same situation and want to link me in into this topic:

In my case, I too have the SMT1500I Smart UPS which is connected on the USB port to my Server, which runs the Powerchute Business Server and Agent so that a clean shutdown is possible.

Now I want to be able to also shut down my Workstation, which is also powered by theUPS, gracefully. But this workstation doesnt have a seriell port. For that reason i purchased the AP9827 cable, which is also listed as optional communication on the product page (see attachment). So i doubt the statement above, that the AP9827 cable doen't work with the SMT model is right. However, on installting the Powerchute Agent on the workstation, it doesnt recognize the UPS and no communication is established...

I have to say, that i bought the AP9827 cable on Amazon (APC UPS Datenanschlusskabel extern USB auf RJ45: Amazon.de: Computer & Zubehör) and on the cable it is printed 940-0127E. Well is this the "right" AP9827 cable? Or is the pinning wrong? Would I get an other cable if i buy directly from apc?

What can i do to get a gracefull shutdown working on my workstation without buying an huge expensiv network management card or seriell port card for my workstation? (besides my server has no seriell port, too.)

Thanks.2147_ap9827.JPG

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

Hi,

AP9827 is the sales SKU and 940-0127E is the manufacturing part number so they are 1 in the same.

As for compatibility with the SMT, I have tested the cable and find it to not be compatible. I will verify this information with product management and up date this thread.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

Hi,

so any news so far? Cause I'm about to send the cable back to Amazon and need clarification. Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

I have verification that the cable is not compatible with the Smart-UPS. It was mistakenly entered as an option on the web site. Our web services team is working to correct the error.

We apologize for any inconvenience.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:59 AM . Last Modified: ‎2024-03-13 11:35 PM

Well....thats really really odd....Will there be another cable that will work with the RJ45 to USB or ist there one in planning? Cause I can't believe ist a brand new UPS an we write the year 2014 and it is not possible to conect more that one Server via USB which is delivered with a Software that supports up to 5 Agents...

Thanks for your Feedback and help anyways.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.