Is there a way to reboot a Symmetra LX while in bypass?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is there a way to reboot a Symmetra LX while in bypass?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:29 AM

0 Likes
3
2194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:29 AM

Is there a way to reboot a Symmetra LX while in bypass?

I want to be able to reboot the Symmetra while having the unit in manual maintenance bypass. The idea is to be able to reboot he UPS but not interrupt power to the connected devices while doing so.

Anyone have any experience with this?

Thanks,E

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:29 AM

0 Likes
0
2192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:29 AM

Yes, while in manual bypass (breaker switch to right of front display pushed to the right), you may cycle the system enable switch on the rear of the UPS without interrupting your load. Once the UPS is rebooted and the display has come back to the way it was, you can flip the same bypass breaker to the LEFT/off position and the UPS will transition on-line without load interruption.

Just curious, but how do you "know" the UPS is not being overloaded on one of its two phases?

On the Symmetra LX, each hot wire output is measured discretely. If your load is comprised of primarily 120v loads, it's possible to load up one of these two hot wires to 100% of their capacity (50% of the total system capacity). The UPS will report the higher of the two phases unless you dig into the detailed Status it provides.

It might be a good idea to find out what your load balance situation is on this split-phase UPS. You can go to the UPS display Status menu and on the fourth page (hit the down arrow 3 times), you will see "% Load Assuming No Redundancy" and two percentage readings on the bottom line. Ideally, these would be close together, so that you may utilize the total capacity of the UPS and not prematurely overload one half of the system.

Let us know what you have there (or get the same data from the Network Management Card). It would be good to know what kinds of equipment you are powering, as well as the number of power modules installed in the UPS. Perhaps you could also provide a sample of the network card's event and data logs for analysis, as well as the Master firmware revision on your Intelligence Modules.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:29 AM

0 Likes
0
2192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:29 AM

unfortunately, i cannot thing of a way to reboot the symmetra LX without disruption to the load without going to manual bypass. any other way will disrupt power to the load.

just to be clear, why do you need to do this? i just want to make sure because if you need to reboot the network interface or possibly one of the other modules or powerview menu, you can do this without rebooting the entire UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:29 AM

0 Likes
0
2192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:29 AM

I am getting some erroneous load threshold alerts (Critical - UPS: The load exceeds 100% of rated capacity.) when I know the UPS load is not exceeding more than 50%.

We have just recently installed 3 more power modules and I wanted to reboot the Symmetra WITHOUT interrupting power to the devices already connected to it.

So to be more clear, I want to reboot the UPS, I am OK with putting it into manual bypass while doing so, provided that while the UPS is in manual bypass it will continue to provide power to the devices while the UPS reboots.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:29 AM

0 Likes
0
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:29 AM

Yes, while in manual bypass (breaker switch to right of front display pushed to the right), you may cycle the system enable switch on the rear of the UPS without interrupting your load. Once the UPS is rebooted and the display has come back to the way it was, you can flip the same bypass breaker to the LEFT/off position and the UPS will transition on-line without load interruption.

Just curious, but how do you "know" the UPS is not being overloaded on one of its two phases?

On the Symmetra LX, each hot wire output is measured discretely. If your load is comprised of primarily 120v loads, it's possible to load up one of these two hot wires to 100% of their capacity (50% of the total system capacity). The UPS will report the higher of the two phases unless you dig into the detailed Status it provides.

It might be a good idea to find out what your load balance situation is on this split-phase UPS. You can go to the UPS display Status menu and on the fourth page (hit the down arrow 3 times), you will see "% Load Assuming No Redundancy" and two percentage readings on the bottom line. Ideally, these would be close together, so that you may utilize the total capacity of the UPS and not prematurely overload one half of the system.

Let us know what you have there (or get the same data from the Network Management Card). It would be good to know what kinds of equipment you are powering, as well as the number of power modules installed in the UPS. Perhaps you could also provide a sample of the network card's event and data logs for analysis, as well as the Master firmware revision on your Intelligence Modules.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of