Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Interpreting "Raw Status Data" of SYPM10KF and SYPM10KF2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Interpreting "Raw Status Data" of SYPM10KF and SYPM10KF2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
162
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ojfsdi
ojfsdi
Contributor

Posted: ‎2022-06-06 04:38 PM

0 Likes
1
2935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-06 04:38 PM

Interpreting "Raw Status Data" of SYPM10KF and SYPM10KF2

I have several SYPM10KF and SYPM10KF2 power modules in a 3phase Symetra 80k.

 

One of the power modules has shown up before as Failed and offline, but usually it is "On & Ok".

 

On a recent such cycle, I took note of the "Raw Status Data" visible in the NMC.

 

Visited UPS because module was reporting "Off and failed", but fans were spinning.  There was no red led, code was: A6 0E 08 00 00 - 00 00 00 00 00 00 - 00 00 00 00 00
then after 4 power cycles, it reads off and ok
00 0C 00 00 00 - 00 00 40 00 00 00 - 00 00 00 00 00
and then a few second later still off and ok, but shows:
00 0C 09 00 00 - 00 00 00 00 00 00 - 00 00 00 00 00
then a few seconds later on and ok and these codes:
07 0F 08 00 00 - 00 00 00 00 00 00 - 00 00 00 00 00

 

All modules are "On & OK" now and read 07 0f 08 and all zero's now. That's for both the old sypm10kf and the new sypm10kf2 mofules.  And for multiple firmware versions.

 

How can I update the firmware on all of my power modules to be the same version?

 

And how can I interpret the "Raw Status Data" of these modules, to better understand what's happening inside the one wild module when it kicks offline?

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
al_buffington
al_buffington Contributor
Contributor

Posted: ‎2022-06-08 08:24 AM

0 Likes
0
2907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 08:24 AM

Hi,

 

There is not a publicly released tool to decode the raw status on a Symmetra PX. I can tell you, based on the codes that you have provided, that the inverter in that power module is locking out due to an error. The "07 0F 08" observed on the last line is typical of a working module. I think it's likely that this module may lock itself out again in the future. My recommendation would be to plan for an eventual replacement. 

 

The hardware is not the same on a SYPM10KF2 &  SYPM10KF. The firmware on those will never match each other. The firmware on the SYPM10KF is not field upgradeable. The firmware can be field updated for the KF2 (by Schneider FSRs only) but only when installed in a Symmetra PX 100k system.  It's unlikely that the KF2s even need an update. There has not been a release of the PM firmware in many years.  

 

Hope this helps.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
al_buffington
al_buffington Contributor
Contributor

Posted: ‎2022-06-08 08:24 AM

0 Likes
0
2908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-08 08:24 AM

Hi,

 

There is not a publicly released tool to decode the raw status on a Symmetra PX. I can tell you, based on the codes that you have provided, that the inverter in that power module is locking out due to an error. The "07 0F 08" observed on the last line is typical of a working module. I think it's likely that this module may lock itself out again in the future. My recommendation would be to plan for an eventual replacement. 

 

The hardware is not the same on a SYPM10KF2 &  SYPM10KF. The firmware on those will never match each other. The firmware on the SYPM10KF is not field upgradeable. The firmware can be field updated for the KF2 (by Schneider FSRs only) but only when installed in a Symmetra PX 100k system.  It's unlikely that the KF2s even need an update. There has not been a release of the PM firmware in many years.  

 

Hope this helps.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore