InRow AC ACRP102 Runtime Balancing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • InRow AC ACRP102 Runtime Balancing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
13
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

InRow AC ACRP102 Runtime Balancing

Hi,

I have 2 InRow ACRP102 Air Conditioners in a HACS and am trying to implement runtime balancing between the two. I have tried to configure them as per the Operations Manual, but so far no luck with an automatic changeover of roles.

Can any one help? I can provide more detail and even the logs if it would help figure out where I'm going wrong.

Regards,

Peter

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:18 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:18 AM . Last Modified: ‎2024-02-14 11:05 PM

Great to hear we got it solved. If you have any issues in the future please let us know.

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

Hello Peter. A few things to check. First under the group configuration, make sure there are two units in the group. Put 1 backup unit but leave the "full RP backups" at 0. Make sure to enable the runtime balance on the units. Also check your Type. If the units are in InRow mode, there is no lead/lag on the units. The units will need to be in HACS or RACS (this depends on the setup of your room. If you have a hot aisle containment system then use HACS. If not use RACS. Next go under the unit configuration and make sure the "role override" is disabled (this will make a unit the primary and run it all the time if it is enabled). Lastly go to the runhours page and clear the runhours for the compressor and the system to get both units to 0. This will get the units on the the same starting point for the runtime balance. The first unit should run for 72 hours then switch over to the second. That one will run for around 144 hours (72 hours past the other) then switch back to the first. They should then continue the switching off about every 6 days form there.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

I am sorry I missed that you are already in HACS so please ignore the Type setup.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

Hi,

Thanks a lot for your prompt response. I had already done most of what you've suggested except I only reset the system runtime, not the compressors'. Let me reset them both to 0 and wait for 72 hours then I will let you know how it goes (fingers crossed it works!).

Thanks again and best regards,

Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

Thank you Peter. Let us know how it goes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:06 PM

Hi,

So after following your advice and waiting 72 hours, the AC units still did not changeover automatically. Now the primary unit has an error "No backup units available exists" but I think the A-Link connection is okay (when I disconnect it I get a "Group communication lost" warning). I have attached latest config files and event logs for both AC units and I would really appreciate it if you could go through them. Maybe they can help pinpoint the problem. Please be in touch if you need more information or clarification about the ACs.

I await your valuable feedback.

Thanks and best regards,

Peter

Attachments
LOGS 5 29 17.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

Hello Peter. From the logs it shows unit 3 as in Standby. This means the unit is manually turned off and will not come on. Make sure to put this unit as on form the front screen. Both units need to be on for then to start the lead/lag. When you look on the front screens one should say on and one should say backup for them to switch over.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

Hello,

Please explain how will they change roles if they are both ON? Will that not result in similar runtimes? Or it can be ON without actually supporting the load?

In the menu presently there are only ON/STANDBY options available. And since the data center installed capacity can be supported by one AC unit, we wanted one unit to run while the other acts as a backup, ONLY coming ON when the primary AC fails or cant handle the installed load for whatever reason.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

Hello. The Standby mode is where the unit has been manually told to stay off. It will never come on to support the load until it is manually turned to "ON" from the front screen. When the unit is turned to "ON" it will be able to support the load. When the unit is by itself and in the ON mode it will run to satisfy the settings that were put on it to cool the room. When the unit is in a group of units with a backup enabled, the units will look at all the units in the group that are turned to ON and will choose one to be in backup mode. This unit in backup mode will not cool unless it is called for to start cooling by either 1. a unit that is cooling that has failed, 2. the units that are cooling are not able to keep up with the load so it will call the backup unit to come on to assist. (you will need to make sure load assist is enabled on the units under group config.) or 3. the runtime balance is enabled and it has reached the time to switch over. This will select another unit in the group to go to backup and turn the backup unit on.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

Hi,

And to enable a backup in the group of units I just configure Num of Units & Num of Backups in the Group Configuration, right?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

Hello Peter. Yes that will set one unit as the backup and one as the primary. If you want the backup unit to come on if the primary unit can not keep up with the load, make sure load assist is enabled. If you would like them to switch over, make sure run-time balance is enabled. Let us know if they are still giving you issues.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

Thanks a lot, I will make the config changes and let you know how it goes.

Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:17 AM . Last Modified: ‎2024-02-14 11:05 PM

Hi,

I'm glad to say it has worked and we had a successful automatic changeover of roles between the 2 ACs.

I appreciate all your help in this matter, thanks a lot!!

Regards,

Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:18 AM . Last Modified: ‎2024-02-14 11:05 PM

0 Likes
0
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:18 AM . Last Modified: ‎2024-02-14 11:05 PM

Great to hear we got it solved. If you have any issues in the future please let us know.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of