Posted: 2023-11-1510:51 AM
1.0.0 works better but APc will not allow you to create your own Certs. they must be created though the NMCSecurity wizard, then signed by your CA, and lastly that signed cert and the originally created key ran back though the NMCSecurity wizard to create a new .p15 file.