Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84439members
353639posts

How can something so easy be so difficult

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
StefanTh
Crewman
Crewman

How can something so easy be so difficult

Why is it so difficult to get a UPS and a couple servers to work together?

 

We have a Smart-UPS (SRT 10000) with web-gui and  Ethernet connected to the rack's main switch.

We have a couple servers with Ubuntu in the rack

The UPS is sending status packages, which are visible on the net, according to the format MASTATUS<body>....</body> every 20 seconds or so

 

What we want: if the battery goes down under 20% or if it is 10% left on the time we want the servers to shutdown gracefully.

 

This simple task seems to be impossible to do.

 

----

 

aopcupsd:

No, not working because the UPS seems to have changed the protocol to  MASTATUS<body>....</body> which apcupsd can not handle correctly.

 

Powerchute:

No, it is only rpm packages (that is for red hat or SuSe)

Convert rpm into .deb? Well almost, because some shebang missing for !/bin/bash, there are errors about [[ statements in shell files etc.

Force convert it into .deb, do the installation and ignoring the warnings about [[

Will it work??? Of course not, when setting up powerchute (which of course is not named powerchute anymore but pcbeagent instead .....) the pcbeagent can only handle usb/serial cables during the setup.

 

NUT:

Have not even tried, when both apcupsd and Schneiders own software (powerchute/pcbeagent) fail this simple use case I do not even want to test,

 

It astonish me that that these things do not work out of the box or in a very simple way.

 

Schneider change the broadcast format so apcupsd no longer work, why ?

Schnedier make the software Powerchute which it is not, it is actually called pcbeagent, why ?

Why can not pcbeagent handle an Ethernet connection to the UPS during setup, why does it insist on usb/serial?

 

 

95% of the use cases of UPS's are very very very simple

Main power loss -> switch to battery

Before running out of battery -> graceful shutdown.

 

 

Regards

 

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator

Re: How can something so easy be so difficult

@StefanTh 

 

 

The UPS ships with a built-in network management card (NMC) compatible with PowerChute Network Shutdown. PowerChute Network Shutdown can be configured to listen to the NMC and will command the OS/servers down when runtime falls below X time. 

 

Here is a link to the PowerChute web page to download the software free of charge. 

https://www.apc.com/shop/us/en/products/PowerChute-Network-Shutdown-v4-4-1-64-bit-systems-only-/P-SF...

 

The installation and user's guides will be found at the same link.

 

See Answer In Context

Tags (1)
2 Replies 2
BillP
Administrator Administrator
Administrator

Re: How can something so easy be so difficult

@StefanTh 

 

 

The UPS ships with a built-in network management card (NMC) compatible with PowerChute Network Shutdown. PowerChute Network Shutdown can be configured to listen to the NMC and will command the OS/servers down when runtime falls below X time. 

 

Here is a link to the PowerChute web page to download the software free of charge. 

https://www.apc.com/shop/us/en/products/PowerChute-Network-Shutdown-v4-4-1-64-bit-systems-only-/P-SF...

 

The installation and user's guides will be found at the same link.

 

Tags (1)
StefanTh
Crewman
Crewman
0 Likes
0
273

Re: How can something so easy be so difficult

Hi

 

PowerChute Network Shutdown

 

Yes, PCNS seems to work, thanks a lot.

 

Notice that on mySchneider Home (se.com)

Only version 4.2 and 4.3 is linked under "firmware", not 4.4 (4.3 is only 32 bit Linux variant)

However it seems that 4.4 works on ubuntu, I will carry out some tests

 

Regards

 

 

 

 

 

Tags (1)