Hetergeneous batteries in Symmetra PX

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Hetergeneous batteries in Symmetra PX
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
118
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-14 08:54 PM

0 Likes
1
972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 08:54 PM

Hetergeneous batteries in Symmetra PX

My PX 80 has 2-year-old 7.2 AH batteries, and some of them are starting to fail a little early.  They are all the same model number, but I've noticed that there is some variation in the markings indicating perhaps not all or them were made in the same location or on the same assembly line.  I'm actually not entirely sure what the minor markings mean.

 

I've examined the SYBTU1-PLP cartridges after they showed a fault condition, and found some of the batteries inside melted a little!  I carefully extricated the damaged batteries, and I've sourced two 8AH replacements from different manufacturers.  The cheaper ones are harder to get quickly, and the more expensive ones come from a supply house across the street, so I have some of each.

 

    Stamping   MaxVoltage RegulationDamage      
         ChargeStandby UseCycle UseBelow      
CodeManufacturerModel tabssideVoltAhHRCurr.LowHiInit. Curr.LowHiVoltageUPCMade InTabs   
AAApexAPX1270 AY11AJS2A180521127               
ABApexAPX1270 BY11AIY1A17112812720 13.713.9<2.114.614.8 6 83405 42858 9ChinaF2 (Large)Constant Voltage ChargeValve Regu. RechargableNonspillable
AHHApexAPX1270 HHY11AIWaA171128127          ChinaF2 (Large)   
AHFApexAPX1270 HHY11AIWbA171128127          ChinaF2 (Large)   
BBright Way GroupBW1280HX12-8(none)052621FH128?????13.613.81.22.414.514.910.58 48050 00170 3ChinaF2 (Large)Replace every 3.5 yearsSealed Lead-Acid BatteryNonspillable
IInterstate BatteriesSLA1079 (none)HVDUL128202.413.513.8??????14.415???6 56489 06612 1VietnamF2 (Large) Sealed Maintenance FreeNonspillable AGM

 

 

I'm wondering what consensus is on mixing different batteries in the same cartridge, 'cartridge pair' A&B or C&D, and shelf.

 

So far I intend to avoid:

  • using different models (which includes amp hours) or ages of batteries in the same cartridge
  • using different modeled or aged cartridges on the same 'cartridge pair'

 

And I intend to keep:

  • the same 'blend' of modeled and aged cartridges in the left side (A&B) as is in the right side (C&D) of the battery frame.

 

Assuming I keep my cartridges clearly marked and labeled, Should I worry about keeping both pairs on the same SHELF identical? 

Or does that not matter itself as long as the blend on all the left shelves is equal to the blend on all the right shelves.

 

In other words, I'm pretty sure it would be bad for all of the left side to be type a batteries and all of the right side to be type b.  But if half of the cartridge pairs are a and half are b, does it matter on what shelf number I put them on as long as the left side has the same ratio of  a to b as the right side has?

 

Also, assuming I keep the 'blends' the same on the left and on the right, should I worry about introducing 8AH batteries into a PX that has only known 7.2's?

 

As you can see in the data table I put together above, the voltage regulation varies a little between each of these batteries.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-11-02 05:55 AM

0 Likes
0
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-02 05:55 AM

Hi,

 

Please refer to the following knowledge base article on the subject of users replacing the individual batteries inside the module:

 

https://www.apc.com/us/en/faqs/FA279266/

 
Regarding the pairing of batteries based on "type" this article should help you:
 
https://www.apc.com/us/en/faqs/FA231261/
 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of