Help with making sense of all of this

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help with making sense of all of this
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
1
569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:39 AM . Last Modified: ‎2024-02-29 11:07 PM

Help with making sense of all of this

Hi All

I have read a fair bit if th e PCNS and management card documentation and I am struggling to make sens of a few things. At risk of sounding as if I have had my frontal lobe removed please see my questions below: My environment is pretty simple:

  • 2 x Standa Alone VMWARE ESXI servers each running the PCNS OVA.
  • 3 x physical servers each running PCNS 4.0
  • Smart-UPS SRT 5000 Firmware - UPS 04.1 (ID1013)
  • NMC AP9537SUM Hardware Revision 05
  • PowerChute Network Shutdown 4.0.0 Build 6078

I am confused with regard to a few things. Please see below:

  • Firstly I am trying to configure the runtime levels for triggering shutdown events on my agents.I assume this gets done under /Configuration/Shutdown. But the settings are not making much sense to me. I would like to configure the clients to shut down should the ups reach 20% remaingin runtime, I estimate this to be around 20 minutes. 
  • It would be great if I could find an explanation of each of these settings under /Configuration/Shut Down
    • Start of Shutdown
      • Low Battery Duration:
      • Maximum Required Delay:
      • Basic Signaling Shutdown:
      • Basic Low Battery Duration:
    • Duration of Shutdown
      • Sleep Time:
    • Sync Control Shutdown
      • Shutdown Delay:
      • Return Delay:
      • PowerChute Shutdown Parameters
      • Maximum Required Delay:
  • I want the UPS to only shut down once all connected servers have been shut down and the UPS has only 5% remaining in order to keep my other devices up and running such as an analogue PABX.
  • PCNS Configurations below:
  • I also noticed that on each PCNS running you are able to configure events, this is a bit confusing for me as certain configurable items would relate to a UPS event that would be duplicated if configured on each PCNS such as email alert on UPS on battery. Or am I missing somethig here.
  • Also under shut down settings the only option is to shut down the UPS, should this not be configured on the UPS NMC itself rather than risking the possibilty of conflicting configurations due to the same setting being conigured on each PCNS?
  • Under Configure Events, what is the difference between Runtime Exceeded and Runtime Below Threshold?

I am sorry fo the long winded question and apologies in advance if i missed something in the docs...

Bash

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:07 PM

Bash,

On 5/28/2015 2:59 AM, Bashir said:

Firstly I am trying to configure the runtime levels for triggering shutdown events on my agents.I assume this gets done under /Configuration/Shutdown. But the settings are not making much sense to me. I would like to configure the clients to shut down should the ups reach 20% remaingin runtime, I estimate this to be around 20 minutes. 

You can configure the shutdown of the PCNS Agents using the NMC by using load shedding. Log into the NMC and go to Configure - Outlet Groups - select an outlet group. Set the outlet group to power down after the power failure last for x minutes or when runtime remaining is less than x. You will find a description of these setting in the NMC help file.

 

On 5/28/2015 2:59 AM, Bashir said:

It would be great if I could find an explanation of each of these settings under /Configuration/Shut Down

  • Start of Shutdown
    • Low Battery Duration:
    • Maximum Required Delay:
    • Basic Signaling Shutdown:
    • Basic Low Battery Duration:
  • Duration of Shutdown
    • Sleep Time:
  • Sync Control Shutdown
    • Shutdown Delay:
    • Return Delay:
    • PowerChute Shutdown Parameters
    • Maximum Required Delay:

The above settings for the NMC are described in the NMC help file.

You should set the low battery setting to be at least 2 minutes longer that the greatest amount of time the servers take to power off. Example: if 4 of the servers take 5 minute to power down and 1 take 10 minutes low battery should be set to 12 minutes. When and if the UPS hits low battery all PCNS agent are sent a shutdown command. This is a failsafe to be sure the servers are shut down safely prior to the UPS running out of battery power.

On 5/28/2015 2:59 AM, Bashir said:

I also noticed that on each PCNS running you are able to configure events, this is a bit confusing for me as certain configurable items would relate to a UPS event that would be duplicated if configured on each PCNS such as email alert on UPS on battery. Or am I missing somethig here.

If you are using load shedding in the NMC and the low battery setting is correct you do not need to configure any events in PCNS. It is your choose as to which way you want to configure your setup.

On 5/28/2015 2:59 AM, Bashir said:

Also under shut down settings the only option is to shut down the UPS, should this not be configured on the UPS NMC itself rather than risking the possibilty of conflicting configurations due to the same setting being conigured on each PCNS?

Using load shedding you can configure different outlet gorups to power down at different times so you can have the servers go down and then the PABX system at a later time.

On 5/28/2015 2:59 AM, Bashir said:

Under Configure Events, what is the difference between Runtime Exceeded and Runtime Below Threshold?

Runtime exceeded and runtime below threshold are described in the PCNS help file.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:07 PM

0 Likes
0
569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:40 AM . Last Modified: ‎2024-02-29 11:07 PM

Bash,

On 5/28/2015 2:59 AM, Bashir said:

Firstly I am trying to configure the runtime levels for triggering shutdown events on my agents.I assume this gets done under /Configuration/Shutdown. But the settings are not making much sense to me. I would like to configure the clients to shut down should the ups reach 20% remaingin runtime, I estimate this to be around 20 minutes. 

You can configure the shutdown of the PCNS Agents using the NMC by using load shedding. Log into the NMC and go to Configure - Outlet Groups - select an outlet group. Set the outlet group to power down after the power failure last for x minutes or when runtime remaining is less than x. You will find a description of these setting in the NMC help file.

 

On 5/28/2015 2:59 AM, Bashir said:

It would be great if I could find an explanation of each of these settings under /Configuration/Shut Down

  • Start of Shutdown
    • Low Battery Duration:
    • Maximum Required Delay:
    • Basic Signaling Shutdown:
    • Basic Low Battery Duration:
  • Duration of Shutdown
    • Sleep Time:
  • Sync Control Shutdown
    • Shutdown Delay:
    • Return Delay:
    • PowerChute Shutdown Parameters
    • Maximum Required Delay:

The above settings for the NMC are described in the NMC help file.

You should set the low battery setting to be at least 2 minutes longer that the greatest amount of time the servers take to power off. Example: if 4 of the servers take 5 minute to power down and 1 take 10 minutes low battery should be set to 12 minutes. When and if the UPS hits low battery all PCNS agent are sent a shutdown command. This is a failsafe to be sure the servers are shut down safely prior to the UPS running out of battery power.

On 5/28/2015 2:59 AM, Bashir said:

I also noticed that on each PCNS running you are able to configure events, this is a bit confusing for me as certain configurable items would relate to a UPS event that would be duplicated if configured on each PCNS such as email alert on UPS on battery. Or am I missing somethig here.

If you are using load shedding in the NMC and the low battery setting is correct you do not need to configure any events in PCNS. It is your choose as to which way you want to configure your setup.

On 5/28/2015 2:59 AM, Bashir said:

Also under shut down settings the only option is to shut down the UPS, should this not be configured on the UPS NMC itself rather than risking the possibilty of conflicting configurations due to the same setting being conigured on each PCNS?

Using load shedding you can configure different outlet gorups to power down at different times so you can have the servers go down and then the PABX system at a later time.

On 5/28/2015 2:59 AM, Bashir said:

Under Configure Events, what is the difference between Runtime Exceeded and Runtime Below Threshold?

Runtime exceeded and runtime below threshold are described in the PCNS help file.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now