Help with a configuration?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help with a configuration?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:41 AM . Last Modified: ‎2024-03-18 04:12 AM

0 Likes
3
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:41 AM . Last Modified: ‎2024-03-18 04:12 AM

Help with a configuration?

Hello all!
I'm in the process of specing equipment for a new server room. I plan on having 2x Netshelter SXs with Rack Air Removal Units on the back (ACF400)

My issue... The servers will be protected by an Inergen Fire Suppression system, in order for this system to be effective/be certified, the room must be air tight when the suppression system activates. Ergo, the ACF400s need to shutdown. This is not a problem as I have already been in contact with SimplexGrinnell and they say it can be done without issue.

My problem. When the ACF400s shutdown I obivously need all servers in the effected racks to shutdown. I have spoken with APC Sales support over the phone and they recommend doing this via PowerChute Network Shutdown triggered by a thermal event. This is all well and great, but I am planning on migrating to Symmetras in the future and not having UPSs in the racks. (Infact a Symmetra will be powering the ACF400s)

Second option is using NetBotz gear, however APC Sales support has indicated that I will need to purchase ISX Central Basic edition ($3,500) in order to fully integrate the NetBotz thermal sensors to trigger a mass server shutdown.


Does anyone have any other ideas for a shutdown? I'm thinking about a dry contact system (triggered by the SimplexGrinnell alarm panel) that will then feed into a Smartslot card.... Is this even possible..?

Any help?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

0 Likes
0
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

Thanks for the reply!

I called back APC tonight because this was bugging the piss out of me. According to the person I spoke with we need to use a NMC w/Environmental Monitoring as this has an I/O block, lucky us, the Symmetra comes with one.

She noted that her tech said that the NO/NC is config'd via the web GUI, next we need to install PowerChute Network Shutdown on all required nodes and it can be configured to read the specific NMC and trigger a shutdown event when the NO becomes closed (or vice versa)

I knew we weren't re-inventing the wheel. 🙂

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

0 Likes
0
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

Using PCNS to trigger the shutdown on dry contacts... of course. I should've known 🙂 Thanks for the info.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

0 Likes
0
538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

Yes, you can do it using a network management card, however I believe (someone correct me if I'm wrong) that the input contacts on the network management card today cannot directly initiate a shutdown. That may be changing in the future.

The indirect route is to use the dry contacts on the NMC to monitor the fire suppression system and send a trap to your network management system when the contact is triggered. The network management system, upon receiving the trap, should then use SNMP to tell the NMC to perform a shutdown. We have instruction on shutting down the UPS via SNMP here and to summarize, grab the [Net-SNMP|http://net-snmp.sourceforge.net/] toolset and do something like this:

snmpset -c public -v 1 IP_of_ups 1.3.6.1.4.1.318.1.1.1.6.2.1.0 i 3

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

0 Likes
0
539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:12 AM

Thanks for the reply!

I called back APC tonight because this was bugging the piss out of me. According to the person I spoke with we need to use a NMC w/Environmental Monitoring as this has an I/O block, lucky us, the Symmetra comes with one.

She noted that her tech said that the NO/NC is config'd via the web GUI, next we need to install PowerChute Network Shutdown on all required nodes and it can be configured to read the specific NMC and trigger a shutdown event when the NO becomes closed (or vice versa)

I knew we weren't re-inventing the wheel. 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of