Graceful Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Graceful Shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:51 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
8
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:51 AM . Last Modified: β€Ž2024-03-06 02:20 AM

Graceful Shutdown

Hi Folks;

I have a SU 3000 & Powerchute business edition. Today the power failed and the batteries were exhausted. Much to my surprise I found that the single server being protected reported in the event logs that it didn't shut down gracefully.

I went into PC Business Ed to check the configuration but I can't make heads or tails of the options. I recall that when I installed the unit I found a simple FAQ on the APC site describing the shutdown process and I beleive this was what I used when I originally set it up. I can't seem to find it anywhere and I've gone through the KB etc and all I can seem to find is info on network shutdown.

Does anyone recall the KB article I saw or can someone post up a link to configuring graceful shutdown for a UPS protecting a single machine?

Thanks very much!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

That's OK - I appreciate the help that you've tried to provide. I was just advised to look into Eaton - I haven't seen their products in some time but I suspect it would be easier to just change out the APC unit then to spend more time trying and find information on configuring a graceful server shutdown from APC.

Sorry, but you've lost our business.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:51 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:51 AM . Last Modified: β€Ž2024-03-06 02:20 AM

as far as i know, no, there is not one entire document available that encompasses every single piece of software we have and UPS/UPS configuration that we sell along with a walk through on how to set it up - which is what it seems you are looking for.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

OK, so just so that we're clear......

After several decades of manufacturing/selling UPS's with an significant emphasis on graceful server shutdown, APC has no documentation whatsoever on actually configuring graceful server shutdown other then the 'tips' in the Powerchute Business edition software?

Good to know that APC has yet to create a document explaining the shutdown stages of their products during a power failure.....

Maybe it's just me but I'm no longer sure that I picked a Winna.... πŸ˜‰

Message was edited by: marvin-miller

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

hi marvin,

can i ask what version of powerchute business edition you are using? apparently we don't have any specific guides but the newer versions walk you through some set up when you install it but then the powerchute business edition agent software also has some help in the help file as well as on the main pages/event descriptions to explain what each option means and is for.

so in order to get you in the right spot - do you use the web browser to access the PCBE agent directly via https://127.0.0.1:6547 or http://127.0.01:3052 or alternatively remotely via the IP? or do you use the powerchute business edition console in order to access and configure your set up?

i attached some pictures from the agent view. the console view is when you use the purplish GUI via its own window versus a web browser.

lastly, there are a few posts available to explain some stuff on the forum here. i am not having good luck searching but maybe you will. i know we have explained things like Time on Battery Threshold Exceeded and similar if you're interested.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

Hi Winna πŸ™‚

I'm using Business Edition version 9.0.1.606 which I believe is the latest. I use the web browser on that machine to access the settings.
I'm pretty sure APC has several documents about configuring graceful shutdown - I just can't seem to find the KB article that explained the process in more detail or the steps the unit takes during shutdown (and how to configure when it takes them).

Yes, there is a help screen and I do find it pretty useless with respect to configuring/understanding graceful shutdown. That's why the KB article I originally used as a reference for configuring the unit was so helpful. Unfortunately, I can't seem to find anything in the KB other then a million articles on configuring network shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

yeah i searched too and asked the individual who manages PCNS/PCBE tech support what he recommends. essentially, if you install PCBE and forget about it, same with network shutdown too, it should begin a shutdown when the UPS reports a low battery value, which the default is when 2 mins of runtime remain. the other event actions can be configured to shutdown earlier than that if you'd like. then you have all the delays like command file delays and shutdown delays that you add to the end of that timeline.

under server shutdown -> shutdown settings seems to be the next most informative thing.

i will at least pass along the feedback about needing the article since we do have plenty on PCNS it seems.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

Yes, it seems to me that if a person can't understand & intelligently configure the UPS shutdown routine it makes the UPS unusable and data loss is going to be absolutely certain when choosing an APC product.

If that seems harsh it's because I know for a fact that over the years volumes of information have been generated by APC with respect to configuring graceful shutdown and the understanding of it.

So, just so we can be clear, APC has no information at all about configuring graceful server shutdown parameters and the company's position is that we should just choose the defaults because that's good enough for all servers no matter the work load or configuration?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

no, that is not the company's standpoint. we have chosen default settings since we cant satisfy everyone with the default configuration. the next thing we provide is the help file for for software which can help you understand certain configuration setting options available to you, depending on your setup. so, no, i guess we don't have a step by step specific guide for the number of different configurations you can configure with PCBE but the help file and descriptions are there to try and help. tech support here and via phone or email is also available if you need help to understand certain options or have questions.

i don't want it to seem like we provide the software and NO support with it because that is not the case. no, we might not have a kbase article but it can be something that is created easily or at least requested to those folks that manage it and then we can try to assist you with your specific configuration if the resources we do have don't suffice.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 12:52 AM . Last Modified: β€Ž2024-03-06 02:20 AM

That's OK - I appreciate the help that you've tried to provide. I was just advised to look into Eaton - I haven't seen their products in some time but I suspect it would be easier to just change out the APC unit then to spend more time trying and find information on configuring a graceful server shutdown from APC.

Sorry, but you've lost our business.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore