Important Announcement: Community Back to Full Functionality
Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM
This was originally posted on APC forums on 4/14/2017
Hello all,
We have a galaxy 3000 ups that after a restart return charger fault and the battery cb goes off after 5 to 10 seconds of the startup.
The batteries are fully charged, each one reads between 13.3 and 13.5, the whole group reads 320v.
Any idea I appreciate.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM
This reply was originally posted by Bill on APC forums on 4/14/2017
Luis,
I asked our Galaxy support team and they replied
Most likely he has an open battery or connection in his battery string.
They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM
This reply was originally posted by Bill on APC forums on 4/14/2017
Luis,
I asked our Galaxy support team and they replied
Most likely he has an open battery or connection in his battery string.
They recommend you call into 3 phase Tech Support 1-401-789-5735 when prompted press 2 then 4 and then 4 again for 3 phase support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:45 AM
This was originally posted on APC forums on 5/24/2017
You need to measure the voltage of each battery separately, necessarily with a small load of 2-5 watts
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.