New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Galaxy 300 3:1 30 KVA
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-1602:44 AM. Last Modified: 2024-11-1709:59 PM
Galaxy 300 3:1 30 KVA
Hello Dears
i have this galaxy 300 3:1 30KVA UPS and i have installed new battreys and all the inverter is working fine with main utility power line, but when the main line if OFF the UPS does not connected to the battreys, even their is no data in related to the battrey measurment that is the voltagee the current and is not read on the screen in side the setting also when the battrey breaker is OFF their is no alarm showing,
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-3005:37 AM
Hello,
If the unit batteries are recently replaced ,then the SR needs to access the service port to adjust the battery parameters and modify the battery replacement date then perform battery tests to ensure the battery runtime constant calculations is updated on the unit display
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-3005:37 AM
Hello,
If the unit batteries are recently replaced ,then the SR needs to access the service port to adjust the battery parameters and modify the battery replacement date then perform battery tests to ensure the battery runtime constant calculations is updated on the unit display