Firmware update failed on SMT2200RMI2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Firmware update failed on SMT2200RMI2U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
FrankAusNRW
Crewman FrankAusNRW
Crewman

Posted: ‎2024-10-19 03:35 AM . Last Modified: ‎2024-10-19 03:22 PM

0 Likes
7
2368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-19 03:35 AM . Last Modified: ‎2024-10-19 03:22 PM

Firmware update failed on SMT2200RMI2U

Hi there,

I've recently purchased a APC UPS SMT2200RMI2U for my homelab after my old UPS died.

Well, battery pack was dead, batteries replaced and the UPS could be startet.

In addition, this UPS is having a NMC 9630v2 that I was able to reset and login to the WebUI.

The FW on the NMC was outdated, so I updated the NMC 9630v2 to v7.1.2 sucessfully.

Next step was to update the FW on the UPS as this was still the 06.5 version. I've pivked the ID18 "SMT18UPS_15-0.enc" and started the FW update from the WebUI of the NMC to the UPS with no calbles connected to the UPS except the LAN cable to the NMC.

The FW was started to be uploaded to the UPS and nothing happens for the next 30+ minutes. The WebUI was still "uploading", the front panel of the UPS was showing "Upgrade in progress" (German language).

Since I was able to connect to the UPS via FTP client, I've copied the FW file "SMT18UPS_15-0.enc" to the "/tmp" folder, hoping that the UPS will start the upgrade automatically upon reboot, but nothing happens - but the FW file might still be there in the "/tmp" folder.

Non of the keys on the front panel was causing any reaction, so finally I decided to power off the UPS and unplug the battery pack for a while. Plug the battery pack again and power on the system was not restarting the upgrade process or doing anythig else.

The four LEDs on the front are all ON, the display empty. The NMC was telling me that the UPS can not be found, but the WebUI is still working.

Later on I've read that this process was is not ideal, but there was no way back now. 

I've then removed the NMC and tried to get access to the UPS with a console cable and got no answer from the device at all. Console cable was tested and is working fine.

Are there any ideas how to get the UPS up and running again? The appliance is dated back to 2012, so RMA is not an option here.

Somebody was writing to use "xmodem" to establish a connection to the UPS. Any experience on this recommendation, as I have never used xmodem yet?

Thanks in advanced,

Frank

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-25 06:15 AM

In response to FrankAusNRW
1 Like
1
2228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 06:15 AM

Hi Frank,

 

This is probably your only method to recover the system. You’ll quickly understand why the system was bricked! 🤦‍♂️👎

 

As those in APC, are releasing firmware that have zero common sense. As to firmware validation and carry over requirements.

 

https://www.tarball.ca/posts/unbricking-an-apc-smt3000-ups-after-a-failed-firmware-update/

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-21 07:31 AM . Last Modified: ‎2024-10-21 07:33 AM

0 Likes
6
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 07:31 AM . Last Modified: ‎2024-10-21 07:33 AM

Hi Frank,

 

Did you turn off the outputs on the system as instructed to in the APC Firmware FAQ?!?

 

How did you confirm the serial cable operates correctly? Are you able to SSH into the system?

 

If I assume you did turn off the output as outlined. You have a valid serial cable on hand and it does allow you to SSH into the UPS.

 

You may try the following steps and see what happens. 

Power: Disconnect the battery and AC Mains.

 

NMC: Remove the NMC from the unit 

 

USB: Connect a USB cable to the UPS and the target computer that has the FUW (Firmware Update Wizard).

 

Serial: Connect the RS-232 to your computer and the RJ50 directly to the back of the UPS.

 

Power: Reconnect the battery cartridge and apply AC Mains to the system.

 

Launch the FUW and confirm it finds the connected UPS. If you follow the prompts  it will indicate the (Only) valid firmware for the system on hand! ☝️

 

When the software indicates to proceed with the firmware process it may complain / cry about the USB cable. Ignore it for now and press continue than disconnect the USB cable.

 

You may also try to connect the USB cable while the serial cable is attached. Both steps (sometimes) forces the firmware to proceed.

 

Let me know what you see and observe on the computer and UPS LCD (LED). 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

FrankAusNRW
Crewman FrankAusNRW
Crewman

Posted: ‎2024-10-21 08:54 AM

In response to Teken
0 Likes
5
2303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 08:54 AM

Hi Teken,

yes, the outputs have been turned off as described and all devices pluged-off too. The NMC has also been removed.

The serial cable has been tested and is working on another device (a Sophos appliance) perfectly and the COM-port is assigned to it.

Allthough, the last time I was able to SSH into the UPS was during the upgrade process, that lateron failed. 

Currently no connaction via SSH or Telnet can be established.

Battery pack and the power cord have been off now for three days.

 

So I did what you said and put the USB-A/USB-B cable to the UPS and the computer, same with the serial-2-USB cable mentioned above, then reconnected the battery-pack and the power-cord.

After the battery pack was reconnected all 4 LED's on the panel went "ON", the LCD panel left blank.

I've startet the FUW (as admin) and let it go to check the COM ports. When it gets to the serial-2-USB cable the cable indicates some traffic, but finally no connection could be established.

Message from the FUW: "Communication could not be established with the device from this computer. Possible causes: ..." You may know the rest of this message.

The LCD panel is still empty, the LED's are all "ON".

 

Is there some kind of pins on the PCB to perform a BIOS reset when this pins are bridged or something similar? I haven't seen any kind of BIOS battery so far to force a "brain dead" for the UPS - just an idea ...

Thanks & kind reagrds,

Frank

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-22 03:57 AM

In response to FrankAusNRW
0 Likes
4
2302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 03:57 AM

Hi Frank,

 

Did you try to add the USB cable vs just starting the FUW with the USB cable in place?

 

X-Modem is really the next step in trying to recover the unit. There is no battery in the system as it relates to the MCU.

 

The only possible way is to have an identical system on hand and dismount the chip, read it, than write the same to the bad one.

 

Lastly, before you go forward with the other method. Insert the NMC while both the serial & USB are in place.

 

Go to the UPS firmware upgrade tab and see if you can load the file indicated by the FUW.

 

If the system allows you to select and load firmware there’s hope. Obviously if there is a resume button present you’re golden.

 

As stated earlier play around with the USB cable while doing so. As an aside, you may find several threads in this forum about simply leaving the UPS for days while the firmware is loading via NMC.

 

I call this out because there’s a less than 2% that could happen. 

Let me know what happens either way. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

FrankAusNRW
Crewman FrankAusNRW
Crewman

Posted: ‎2024-10-25 05:39 AM

In response to Teken
0 Likes
0
2232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 05:39 AM

Hi Tecken,

I've tried what you recommended to do. Anyhow, the USB-cable was of no help so far, neither the UART serial-cable. At least, the UART serial cable is providing a COM port, but this COM Port doesn't help to run a FW update with the FUW.

With the NMC in place I got again the message, that there is no UPS connected, but I was able to establish a FTP connection (SSH failed) to the NMC - or even the UPS? Don't know ... I've uploaded the FW package to the "/upsfw" folter ... waiting ... waiting ... waiting ... just let it go for a couple of hours, but nothing happened.

So my next apptempt was to shut the UPS down (power cord and battery pack) for an hour and try to trigger the FW update with a restart and the file previousely loaded to the "/upsfw" folder. Again, even after a couple of hours nothing happened.

During the entire process all LEDs on the front have been "ON", and the display remain empty.

 

Turning in circles, I'm running out of ideas. Don't have a second, identical UPS around. Seem to be bricked during the initial FW upgrade started from the NMC panel. It's weired, that so many people like me are trying this way, as it seem to me a standard procedure, but at the end the appliance can hardly be restored.

 

Any more ideas? Would be very much appreciared ...

 

Thanks,

Frank

Reply

Link copied. Please paste this link to share this article on your social media post.

FrankAusNRW
Crewman FrankAusNRW
Crewman

Posted: ‎2024-10-25 05:42 AM

In response to Teken
0 Likes
2
2232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 05:42 AM

2024-10-23 11_57_26-UPS Network Management Card 2.png

Here the log from the NMC from the initial FW upgrade. The file was sucessfully transfered and the connection interupted. Ok, if the UPS is starting the upgrade process, that was confirmed on the front display, the connection to the NMC get lost. So far everything was fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-25 06:15 AM

In response to FrankAusNRW
1 Like
1
2229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-25 06:15 AM

Hi Frank,

 

This is probably your only method to recover the system. You’ll quickly understand why the system was bricked! 🤦‍♂️👎

 

As those in APC, are releasing firmware that have zero common sense. As to firmware validation and carry over requirements.

 

https://www.tarball.ca/posts/unbricking-an-apc-smt3000-ups-after-a-failed-firmware-update/

Reply

Link copied. Please paste this link to share this article on your social media post.

FrankAusNRW
Crewman FrankAusNRW
Crewman

Posted: ‎2024-10-26 04:23 AM

In response to Teken
0 Likes
0
2143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 04:23 AM

Hi Teken,

thank you for the link, I will give it a try at a later point of time. Currently busy with some other topics.

Probably I will need a bid time on my own, and the SMT32 link utility, not yet here on stock.

I will mark your suggestion as "solution".

Appreciate your patience and time you've spend here, even on a 12 year old device - good enough for a second life in my homelab. Thumbs up!

Cheers mate,

Frank

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore