Fan performance warning on ACF402 (Rack Air Removal Unit SX)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Fan performance warning on ACF402 (Rack Air Removal Unit SX)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

0 Likes
4
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

Fan performance warning on ACF402 (Rack Air Removal Unit SX)

Why do I keep on getting 'ARU: Fan X performance warning' messages on the air extraction unit? They clear within 1 second. and then it happens again a few minutes later.

Am I supposed to do some maintenance on the Air Removal Units?!?

Richard.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ACF402
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

Fantastic, thank you very much!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

Hello Richard. Does this alarm stay on just one fan or does it jump around to all the fans? If this is on one fan, make sure the fan is clean and spinning freely. See if any bearing noises are coming from the fan. You can swap the fan with another fan and see if the faults follow the fan or stay in the same slot. If the alarm is on one fan and the alarm follows the fan when it is swapped with another fan then this would point to something on the fan model starting to go bad. If the alarm happens randomly on all the fans, check the connections on the fans and on the electronics model (all this and steps above are to be done with the unit unplugged and no power going to it.) to make sure there is not a loose connection somewhere.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

It jumps to both the active fans, 1 and 4. 2 and 3 are not active. For example:

01/18/2017 15:12:18 ARU: Fan 4 performance warning Cleared
01/18/2017 15:12:18 ARU: Fan 1 performance warning Cleared
01/18/2017 15:12:18 ARU: Fan 4 performance warning
01/18/2017 15:12:18 ARU: Fan 1 performance warning
01/18/2017 15:05:43 ARU: Fan 4 performance warning Cleared
01/18/2017 15:05:43 ARU: Fan 1 performance warning Cleared
01/18/2017 15:05:42 ARU: Fan 4 performance warning
01/18/2017 15:05:42 ARU: Fan 1 performance warning
01/18/2017 14:50:51 ARU: Fan 1 performance warning Cleared
01/18/2017 14:50:50 ARU: Fan 1 performance warning
01/18/2017 14:42:55 ARU: Fan 4 performance warning Cleared
01/18/2017 14:42:55 ARU: Fan 1 performance warning Cleared

..........

Fan 1 Running Ok 1964rpm 639m3/hr
Fan 2 Off & Ok
Fan 3 Off & Ok
Fan 4 Running Ok 1981rpm 644m3/hr

Is there a guide to replacing the fans? I searched everywhere on the support knowledgebase, can't find anything about how to replace fans.

Thanks for your advice!

Richard.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

Hello. Here is the document to replace the fan modules.

Thank you

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:11 AM . Last Modified: ‎2024-03-18 11:36 PM

Fantastic, thank you very much!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of