APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 01:27 AM . Last Modified: 2024-03-18 11:29 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:27 AM . Last Modified: 2024-03-18 11:29 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:27 AM . Last Modified: 2024-03-18 11:29 PM
Hello. The ACSC100 along with most DX cooling units are plugged directly to utility power (no UPS). This is due to the start up draw of the compressor which can over most UPS's unless the UPS is way over sized. To answer the question, plugging the ACSC100 directly to utility power is fine.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:27 AM . Last Modified: 2024-03-18 11:29 PM
Hello. The ACSC100 along with most DX cooling units are plugged directly to utility power (no UPS). This is due to the start up draw of the compressor which can over most UPS's unless the UPS is way over sized. To answer the question, plugging the ACSC100 directly to utility power is fine.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.