Error on Rack Mounted UPS Model AP9630

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Error on Rack Mounted UPS Model AP9630
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:05 AM . Last Modified: ‎2024-03-13 04:25 AM

0 Likes
19
3209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:05 AM . Last Modified: ‎2024-03-13 04:25 AM

Error on Rack Mounted UPS Model AP9630

I recently replaced the battery in my AP9630 Rack mounted APC. Upon swapping the batteries i noticed that the red led next to the Battery with an X through it was blinking and beeping. I did not think anything of it as the documentation says Blinking lights are normal until a device passes its first self test only after the device holds a 75% charge or greater. However its been a full day now and the LED lights indicated charge % are all dark and the beeping has continued. all relevant data is below. The device has a network Management Card and is setup to shut down multiple server on the network and on server via USB connection. No self tests have passed 

Hardware Factory

Model Number: AP9630
Serial Number: XXXXXXXXXXXXX
Hardware Revision: 05
Manufacture Date: 12/03/2014
MAC Address: 00 C0 B7 8A F3 F2
Management Uptime: 0 Days 0 Hours 40 Minutes

Application Module
name: sumx
Version: v6.1.1
Date: Mar 7 2014
Time: 12:05:01

APC OS (AOS)
Name: aos
Version: v6.1.1
Date: Mar 7 2014
Time: 11:52:49

APC Boot Monitor
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57

Critical Alarm Present

02/18/2016 12:14:35 UPS: The local network management interface-to-UPS communication not established

02/18/2016 12:55:57 System NTP update failure.

Emails im receiving from the network card: 

Name : apc8AF3F2

Location : Unknown

Contact  : Unknown

 

http://apc8AF3F2.XXX.com

http://10.1.1.92

http://FE80::2C0:B7FF:FE8A:F3F2

Serial Number : XXXXXXXX

Device Serial Number : NA

Date : 02/18/2016

Time : 12:14:35

Code : 0x0102

 Critical - UPS: The local network management interface-to-UPS communication not established.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

Glad to hear it!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 19
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:05 AM . Last Modified: ‎2024-03-13 04:25 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:05 AM . Last Modified: ‎2024-03-13 04:25 AM

Hi Jordan,

The information you gave to the forum is actually the information regarding the network card, an AP9630, that is installed in your particular UPS and not the UPS itself.

What is the UPS model itself?  There should be a tab on the web interface called "About" and then beneath that a tab called UPS.  In lieu of that, the information can be taken off a label on the back of the UPS itself.

Waiting to hear from you with the UPS information.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:05 AM . Last Modified: ‎2024-03-13 04:25 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:05 AM . Last Modified: ‎2024-03-13 04:25 AM

Hi Joe, Jordon,

It seems the AP9630 UPS Network Management Card (NMC) is reporting it lost internal communication to the UPS so I am guessing About->UPS will be missing or not having information listed. We'll need it from the sticker on the UPS like you suggested.

We'll want to troubleshoot why the AP9630 NMC cannot talk to the UPS in order to get them talking and then understand the condition of the UPS that it can report to us. Knowing the UPS model will be important too along with that. Based on what you described, it sounds like an older unit with no LCD screen and something like an SUA, SURT, SU, SUM type model.

Depending on UPS type, we'll want to make sure it does not have any serial or USB cables connected to the rear of it..only the Ethernet cable to the NMC. Serial or USB cables connected with an NMC installed can cause this problem. Once we know the UPS model too, we can double check if there is anything else along these lines to look at.

The full NMC logs would also be helpful to see the unit's history and how long this issue has been reported. If you can go to the web interface and get to About->Support and can generate logs and download logs, we'd like to see the .tar file. Detailed instructions on getting the logs through this method and others are here -> http://www.schneider-electric.us/en/faqs/FA156131 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:25 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:25 AM

If there is anything I can do about this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:25 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:25 AM

Hi Jordon,

Thanks for all the info.

To start, the architecture and design of the now older SUA model units do not allow for simultaneous communication between USB and serial communication busses. Newer UPS models can handle it though we don't typically recommend it. It'd still work though. The problem is that the UPS SmartSlot (where the AP9630 is installed) is part of the serial communication bus so connecting the USB cable stops the serial bus from working properly. Typically you have to "braindead" the UPS to get it to work again. This means turning the equipment off from the UPS, turning the UPS off itself, and unplugging the UPS from the wall. Then, holding down the off button, which looks like this (o) and the UPS will click and flash its LEDs indicating it has been bread deaded.

What you can try first, since you removed the USB cable now, is rebooting the management interface of the UPS to see if that works. To do that, go to Control Menu->Network->Reset/Reboot and the radio button defaults to the correct option of "Reboot Management Interface" so Apply that, confirm, and let the management interface of the NMC reboot to see if it will start talking to the UPS after it reboots. If it doesn't, you'll have to do the "brain dead option" when you can afford to turn off the server. And, the USB will have to stay disconnected or else you'll get back to where we started again. 

Unfortunately with this UPS, you cannot use the USB and AP9630 at the same time because you'll constantly have this issue and the NMC becomes useless because it cannot operate on the serial bus with the UPS connected. You'll have to either just use AP9630 or just use USB. Alternatively, if the UPS was upgraded to a model with SMT or SMX prefix in their SKU, you could get away with the USB and NMC at the same time as the communication busses on the new units are all isolated and won't interfere.

Let me know if you have any questions.

P.S. the AP9630 firmware is out of date so once you sort out what you want to do, I'd suggest we upgrade this to AOS 6.4.0/sumx app 6.4.0. It has a lot of fixes since what you have (6.1.1) including security related items.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:25 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:25 AM

Sad day. the Net card reboot did not work. it might be time to purchase a smarter smartups.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

Quick question. while i wait for an opportune time to brain dead this APC and bring it back should I be concerned about it functioning correctly? This specific device supports all important Switches and could be disastrous if it went down.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

Hi Jordon,

It's hard to say since the NMC cannot talk to the UPS, we don't know if there are any faults present on the system to be concerned about. In general, if there are also no red LEDs on the front panel of the UPS, there will likely not be an issue. I of course can't be 100% sure but it'd be my educated guess that if the UPS is not acting strange with beeping and red lights, it should be fine to turn it back off and back on again. The only other thing would be to know when the battery was last changed and also, if you know if the UPS self tests (quick battery load tests) have been running in order to catch any battery issues. Sometimes you can run into an issue where a dead/old battery would cause the UPS not to turn on again. That is really worst case scenario though. I don't want to NOT mention anything and then you find a problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

well in my case the unit is beeping. and there are no light light up on the load side. So I probably should be concerned then?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

Oh, yes, you did mention that. I apologize. So the load side is the left bar graph. What other LEDs do you have illuminated and what is their color/flashing pattern? And what is the beeping pattern - chirping, constant tone, 4 beeps every thirty seconds, etc? I also don't know if you have the capability to take a video that we could look at if that is easier?

Here is the UPS front panel LED reference if you need it. Yours should look the same.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

Hi Jordon,

OK, so the load graph is the one on the left. The one with no lights on the right is the battery charge LEDs. And the flashing red LED you have is the replace battery LED. When it is flashing, it means the UPS thinks the battery is disconnected. This means it is physically disconnected which you could verify or that it is "bad" and it is so bad the UPS can't even "see" it anymore so it reports disconnected.

Long story short, you have a battery issue. If the battery is more than 2 years old, it likely actually needs a replacement. If it is relatively new, then it could be physically disconncted or faulty.

I'd start by removing the front bezel and check the blue (I think its blue on this one) connector and make sure it is plugged in. Also check for any swelling or leaking too, just in case, You may want to put the back of your hand on the battery area and see if it is heating up. When you have a battery that is bad like this (assuming it is not unplugged), it could continue charging and cause a problem.

You probably need to plan on a replacement battery for this to swap in or if you were interested, look into an entire UPS upgrade. We can tell how old the UPS is if you find the first six characters of its serial number on the white sticker where you saw the model number. And then with that, understand too if battery is original or was ever replaced since the serial number won't help if the battery was replaced since it was manufactured.

I don't want to tell you to turn the UPS off with this issue because I can't be sure in this state that it will turn back on 100%. I do urge you to investigate this battery issue ASAP as I suggested so we can get it fixed and also get your original issue fixed.

Let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

This Battery is brand new out of the box. so it "shouldn't" be faulty. Since the device is not reading any battery at all would it be safe to say i could unplug the Blue connector and plug it back in while still being live? in case it just didn't seat correctly when i replaced it last week? I feel like this could be possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:06 AM . Last Modified: ‎2024-03-13 04:24 AM

Yep, that should be fine since it is a new battery. I would've suggested caution if it was older and you noticed leaking, swelling, etc. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

So this model is hotswapable then? 

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

Hi Jordan,

Yes the battery is hotswapable on this unit 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

FIXED! the issue was that the cable connecting the new battery and the device was not seated properly. It literally took a hammer to correct the issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

How long did you let the battery charge after you got it re-connected it properly? I'd make sure you let it charge at least 8 hours before running the self test in general and even now before you try again. Keep in mind, the battery was sitting for a bit not charging while it was disconnected so it is possible it could've caused the UPS self test to fail since it sat there not charging for days (weeks). And, if it wasn't at 100% when it was purchased, that could be an issue too.

So, give it a least 8 hours and let's try another self test. Hopefully it will be fine afterwards cool

Otherwise, if it still is a problem and we're confident it was fully charged, it could be replaced (assuming it was a genuine APC branded battery). If you got a different brand battery from somewhere else, they may be able to do the same for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

It is a genuine APC battery. but I will wait another day and run it again. fingers crossed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

Looks like it passed! took about 12 hours to recharge.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

0 Likes
0
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:07 AM . Last Modified: ‎2024-03-13 04:24 AM

Glad to hear it!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore