Email alert, how to report details in email body

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Email alert, how to report details in email body
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

0 Likes
2
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

Email alert, how to report details in email body

Hi, I often get "UPS: Compensating for a low input voltage." type events via email.

How do I change the configuration of so that the email contains the details of the event, specifically what the low voltage was for what duration that caused the event?

E.g. 

Log: 07/29/2016 20:03:38 Device UPS: Compensating for a low input voltage. 0x010B

Email: Warning - UPS: Compensating for a low input voltage.

Data: 07/29/2016      20:02:20    108.69      112.28      109.19      3.13    28.12   24.00   59.99   100.00      54.09   31.67   35.0    

I would like to see the data details, i.e. the 108.96V input to be in the log and email body.

I am using a Smart-UPS X 1500 with a AP9631 network card.

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

0 Likes
0
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

Hi Pieter,

First off, my apologies no one posted earlier. Unfortunately, this isn't an option strictly speaking in the email alerts. However, I'm thinking there may be a way for you to get notified of this if you use SNMP and have a way to set this up on your end. You could get a snmp trap for the same alert - compensating for low input voltage - and have some way of a script getting the input voltage at that time via SNMP (I can look up that OID if you need, but it would be in our standard MIB file). I believe there are some SNMP clients can email you as well, but this whole process may require some coding and time on your end. Hopefully someone else can chime in if they know of a better way to do this, since we don't have an easy way on our end.

Sorry there isn't an straightforward solution, but let me know if you need anything else.

Thanks,

Tommy

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

0 Likes
0
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

APC, possible, not possible?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:46 AM . Last Modified: ‎2024-03-13 01:25 AM

Hi Pieter,

First off, my apologies no one posted earlier. Unfortunately, this isn't an option strictly speaking in the email alerts. However, I'm thinking there may be a way for you to get notified of this if you use SNMP and have a way to set this up on your end. You could get a snmp trap for the same alert - compensating for low input voltage - and have some way of a script getting the input voltage at that time via SNMP (I can look up that OID if you need, but it would be in our standard MIB file). I believe there are some SNMP clients can email you as well, but this whole process may require some coding and time on your end. Hopefully someone else can chime in if they know of a better way to do this, since we don't have an easy way on our end.

Sorry there isn't an straightforward solution, but let me know if you need anything else.

Thanks,

Tommy

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore