I wish to know if there a way to connect an EPO (ISX EPO) to shut down InRow RP DX. I read in the manual something about a input switch shutdown contacts, but I don't know if I can use this to emergency turn off cooling units.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:54 AM . Last Modified: 2024-03-19 01:17 AM
I wish to know if there a way to connect an EPO (ISX EPO) to shut down InRow RP DX. I read in the manual something about a input switch shutdown contacts, but I don't know if I can use this to emergency turn off cooling units.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:54 AM . Last Modified: 2024-03-19 01:17 AM
http://www.apcmedia.com/salestools/ASTE-6Z5SB9_R1_EN.pdf
Read page 44 and 46 for how to use the contacts to remote shut down the cooling units.
*page 44 and 46 on your PDF viewer
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:54 AM . Last Modified: 2024-03-19 01:17 AM
The Inrow cooling units respond to a triggered shut down event. They are not designed to create the event. You would want a general push button EPO to trip your upstream breakers.... Inrow cooling units don't have downstream breakers as they are not power distribution equipment, its an air conditioner.
The Inrow RC does provide a 12 and 24 vdc power supply so you could use that as a Shunt trip through a EPO push button to trip a feeder breaker in theory.
Message was edited by: upsguy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:54 AM . Last Modified: 2024-03-19 01:17 AM
then, could you use this for a EPO to trip the CBs up and downstrean?
thx
Message was edited by: mihail@cpeinc.ca
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:54 AM . Last Modified: 2024-03-19 01:17 AM
I wish to know if there a way to connect an EPO (ISX EPO) to shut down InRow RP DX. I read in the manual something about a input switch shutdown contacts, but I don't know if I can use this to emergency turn off cooling units.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.